Combined footing design in staad - load application

 
Post new topicReply to topic    www.sefindia.org Forum Index -> Freshers' Zone
View previous topic :: View next topic  
Author Message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 110

PostPosted: Fri Apr 13, 2018 10:22 am    Post subject: Combined footing design in staad - load application Reply with quote

Hi All,

Iam designing combined footing in staad using plate elements by assigning support conditions as elastic mat throughout the area of footing.

How to apply load on columns? Is is right if we apply loads of the respective column divided by area of footing as a plate pressure on the column? Please clarify me?

Thank you,
Ramu.
Back to top
View user's profile Send private message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1408
Location: Cochin

PostPosted: Fri Apr 13, 2018 2:16 pm    Post subject: Reply with quote

I think, your proposition is sensible. If we apply column loads as point loads, the analysis is likely to indicate unrealistic concentration of stresses / moments around the point loads. Please ensure that the plate size is so chosen that the column dimensions are multiples of the dimension of the plate, for compatibility in application of column load as UDL.


E S Jayakumar
Back to top
View user's profile Send private message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 110

PostPosted: Sun Apr 15, 2018 12:20 am    Post subject: Reply with quote

Thank you sir.

I have applied each of the column load as pressure(load/Area) and i have attached the staad file for your reference.

Iam little confused to apply the column load as UDL.

Please clarify me which is the correct method to apply loads on column.

Thank you.

Ramu.



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
Combined footing_.zip
 Description:

Download
 Filename:  Combined footing_.zip
 Filesize:  3.68 KB
 Downloaded:  486 Time(s)

Back to top
View user's profile Send private message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1408
Location: Cochin

PostPosted: Sun Apr 15, 2018 5:23 am    Post subject: Reply with quote

I find your column size is 0.70m x 0.20m. Suppose your column load is 1400kN. Then the Plate UDL you have to apply over an area of 0.70m x 0.20m is 1400/(0.70*0.20) = 10000 kN/m2. I think, there is some confusion in your comprehension.

E S Jayakumar
Back to top
View user's profile Send private message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 110

PostPosted: Mon Apr 16, 2018 9:49 am    Post subject: Reply with quote

Thank you sir,understood clearly.After this analysis, we have to design the footing for maximum Mx & My from plate contours,and check for one way and two way shear.Please clarify me.

Thank you
Ramu.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic    www.sefindia.org Forum Index -> Freshers' Zone All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy