Minimum Reinforcement in Pile ?

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
patilamol86
SEFI Member
SEFI Member


Joined: 29 Mar 2010
Posts: 5

PostPosted: Wed Aug 08, 2012 4:07 am    Post subject: Minimum Reinforcement in Pile ? Reply with quote

Dear Friends,

Kindly confirm the minimum reinforcement in pile whether its 0.4% as per IS code or 1.25%  as per books

I have attached the snaps from book BC PUNMIA/RAMAMURTAM they all said same philosophy that 1.25% upto 30D and then increases as per length of pile.

I didnt found these clauses in code which are written in the books but all authors are saying same philosophy it means they are following the same referance.

What is your opinion  ?



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
Foundation Design.pdf
 Description:

Download
 Filename:  Foundation Design.pdf
 Filesize:  155.99 KB
 Downloaded:  1612 Time(s)

Back to top
View user's profile Send private message
er.mvv
General Sponsor
General Sponsor


Joined: 03 Aug 2011
Posts: 86
Location: Hyderabad

PostPosted: Thu Aug 09, 2012 5:40 am    Post subject: Re Reply with quote

Dear Patil

      Minimum % shall be 0.4% as per IS:2911 (Part-1/Sec-2)-1979. Since we follow the codes, you can proceed with the above clause.


best regards
    MVV


Dear SENIOR SAFIANs

         Please comment on the above issue raised by Patil.


best regards
     MVV
Back to top
View user's profile Send private message
patilamol86
SEFI Member
SEFI Member


Joined: 29 Mar 2010
Posts: 5

PostPosted: Fri Aug 10, 2012 3:25 am    Post subject: Reply with quote

Dear SENIOR SAFIANS

Please comment on this Issue
Back to top
View user's profile Send private message
structwell
SEFI Regulars
SEFI Regulars


Joined: 26 Jan 2003
Posts: 20

PostPosted: Fri Aug 10, 2012 5:35 pm    Post subject: minimum reinforcement in pile Reply with quote

Dear Patil


The percentage of steel for Cast in-situ piles min 0.4% of C/s area of pile. Since the reinforcement is not accounted in load calculation of cast in-situ piles. only the unreinforced concrete strength is taken in structural capacity of the pile. For Precast piles the percentage of steel is based on L/D ratio (i.e 1.25%) for withstand the handling stress, driving stress.

Kamaraj.B
Structural Engineer.
Back to top
View user's profile Send private message
patilamol86
SEFI Member
SEFI Member


Joined: 29 Mar 2010
Posts: 5

PostPosted: Mon Aug 13, 2012 4:15 am    Post subject: Reply with quote

Dear Kamaraj

Thank you for your response but in the books they didnt mention the Precast piles they

just wrote RC pile reinforcement.

I appreciate you, if you gave the reference document for this

Regards
Amol Patil
Back to top
View user's profile Send private message
mukeshkumar121in@gmail.co
SEFI Member
SEFI Member


Joined: 02 Jun 2011
Posts: 16

PostPosted: Sat Jun 09, 2018 2:42 pm    Post subject: Minimum reinforcement in pile Reply with quote

Dear Mr Patil
If the pile is bored cast in situ,then the minimum reinforcement required is 0.4 percent of gross cross sectional area as per IS -2911.
If the pile is pre cast,then the reinforcement should be as per IS-2911 part 1 section 3.It depends upon l/D ratio and varies from minimum 1.25 percent to 1.5 percent of cross sectional area.The same is mentioned in BC Punmia Sir book which you have provided as attachment.It is required for lifting and handling stress.
Regards
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy