NEW BUILDING BETWEEN TWO ADJACENT EXISTING BUILDINGS
Goto page Previous  1, 2
 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1162
Location: Cochin

PostPosted: Sat Oct 06, 2018 11:19 am    Post subject: Reply with quote

It is a good suggestion to lift the column position inwards and provide cantilever beams and slab to maintain the required floor area. Provision of raft slabs can be thought of, if the bearing area of strap foundation envisaged is falling short, in that case.

E S Jayakumar
Back to top
View user's profile Send private message
ishata_gupta
SEFI Member
SEFI Member


Joined: 17 Aug 2018
Posts: 6

PostPosted: Mon Oct 08, 2018 10:54 am    Post subject: Thank You for taking out your time to reply! Reply with quote

Yes the buildings are very old and in use.
i was recommended by an experienced structural engineer to chisel the brick foundation for only the width/depth of the column and place the footing just below the existing brick foundation so that the load is transferred from the brickwork to the new concrete footing.
Also i was advised to place dowels in the footing and hammer them in the masonry for load transfer.



es_jayakumar wrote:
Are the adjoining buildings in use ? You have to keep two aspects in mind, in this regard :
1. Chiseling the foundations of the existing buildings will not only reduce the bearing area, but also make the loading on soil eccentric. Impact while chiseling can damage the adjoining portion of masonry also.
2. When you place the new foundation abutting an existing one, the soil may get over-stressed due to merging of pressure bulbs.

E S Jayakumar
Back to top
View user's profile Send private message
ishata_gupta
SEFI Member
SEFI Member


Joined: 17 Aug 2018
Posts: 6

PostPosted: Mon Oct 08, 2018 11:04 am    Post subject: Reply with quote

Yes! The first idea was to shift the columns inward and consider the beams as cantilevered. also since the walls are 13.5" thk, we can have the beams rest on the walls with 7-8" bearing making the beams act as propped cantilevers.

es_jayakumar wrote:
It is a good suggestion to lift the column position inwards and provide cantilever beams and slab to maintain the required floor area. Provision of raft slabs can be thought of, if the bearing area of strap foundation envisaged is falling short, in that case.

E S Jayakumar
Back to top
View user's profile Send private message
ishata_gupta
SEFI Member
SEFI Member


Joined: 17 Aug 2018
Posts: 6

PostPosted: Mon Oct 08, 2018 11:11 am    Post subject: Re: NEW BUILDING BETWEEN TWO ADJACENT EXISTING BUILDINGS Reply with quote

i was recommended by an experienced structural engineer to chisel the brick foundation for only the width/depth of the column and place the footing just below the existing brick foundation so that the load is transferred from the brickwork to the new concrete footing.
Also i was advised to place dowels in the footing and hammer them in the masonry for load transfer.

ravee6a wrote:
Dear gupta,

Take the advise of local engineer having experience of such foundation
and soil condition of that locality.
A.Raveendran.

Posted via Email
Back to top
View user's profile Send private message
ishata_gupta
SEFI Member
SEFI Member


Joined: 17 Aug 2018
Posts: 6

PostPosted: Mon Oct 08, 2018 11:43 am    Post subject: Re: Border restraint Reply with quote

Thank you for your response Mr. Suraj Sir.

Due to lack of soil report, i'm assuming SBC as 13t/sqm at 5' below NGL (the value usually considered for the soil in this area).


suraj wrote:
Better design a combined footing
Why go 4.5 feet below NGL?
What is value of SBC?
It is OK just to found building at a depth around 1M, if SBC permits
If it is required, apply soil improvement method to raise soil BC
This common wall problem is too old & not required, but authorities do not think
You can also, opt for beam foundation connecting all columns if Combined Footing is not desired
Design as structural beams shall provided a better foundation
Columns to come up from top of beams, with reinforcing starter bars from base of beam
Spread isolated footing not necessary
Back to top
View user's profile Send private message
ishata_gupta
SEFI Member
SEFI Member


Joined: 17 Aug 2018
Posts: 6

PostPosted: Mon Oct 08, 2018 11:46 am    Post subject: Re: NEW BUILDING BETWEEN TWO ADJACENT EXISTING BUILDINGS Reply with quote

Yes! The first idea was to shift the columns inward and consider the beams as cantilevered. also since the walls are 13.5" thk, we can have the beams rest on the walls with 7-8" bearing making the beams act as propped cantilevers.
But then i was told that this chiseling of brick foundation for column footing is a very common practice in case of common load bearing walls.

[quote="prof.dsp"]It's better to avoid chiseling by shifting the columns inwards.

On 6 Oct 2018 06:29, hemaraj rv <forum> wrote:
Quote:
       check the soil property and if possible construct same brick foundation partially for adjacenrt columns  On Wed, Oct 3, 2018 at 3:53 PM ishata_gupta forum@sefindia.org)> wrote:  --auto removed--

Posted via Email


Back to top
View user's profile Send private message
suraj
General Sponsor
General Sponsor


Joined: 17 Apr 2008
Posts: 1965
Location: NCR Faridabad, E mail suraj_engineer@yahoo.co.uk

PostPosted: Sat Oct 13, 2018 12:51 am    Post subject: Re: Border restraint Reply with quote

If you are sure that SBC is adequate to found at 1M level below NGL, better go for combined footing. Make sure that it is not clay & if it is, better provide soil improvement first

ishata_gupta wrote:
Thank you for your response Mr. Suraj Sir.
Due to lack of soil report, i'm assuming SBC as 13t/sqm at 5' below NGL (the value usually considered for the soil in this area).


suraj wrote:
Better design a combined footing
Why go 4.5 feet below NGL?
What is value of SBC?
It is OK just to found building at a depth around 1M, if SBC permits
If it is required, apply soil improvement method to raise soil BC
This common wall problem is too old & not required, but authorities do not think
You can also, opt for beam foundation connecting all columns if Combined Footing is not desired
Design as structural beams shall provided a better foundation
Columns to come up from top of beams, with reinforcing starter bars from base of beam
Spread isolated footing not necessary
Back to top
View user's profile Send private message Visit poster's website
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy