Hi All,
How to calculate the punching shear in eccentric footing(column located at the edge) ?
Please refer the attachment and clarify how the punching shear behaviour in plan-1 & plan-2 footing?
Thank you.
Sathya.
 Filesize:  7.91 KB
 Viewed:  44 Time(s)
PostPosted: Fri Oct 25, 2019 9:29 am    Post subject: Reply with quote
First of all, edge or corner columns on an isolated footing is theoretically unstable, as soil will develop tension on the farther side. Hence the proposed arrangement is never advisable to adopt.
For academic interest : In the first case, there is a stiffener beam. Hence, there will be no punching action. In the 2nd case, the punching shear will act at d/2 from the face of the column. The attached Work sheet will be handy for calculations in this connection.
Design of Slab Type Raft or Footing for Moment & Shear.xls
 Filename:  Design of Slab Type Raft or Footing for Moment & Shear.xls
 Filesize:  182.5 KB
 Downloaded:  111 Time(s)
sathyace
PostPosted: Sat Oct 26, 2019 2:01 am    Post subject: Reply with quote
Thank you sir for the valuable reply.
Practically,we get both case of eccentric footing since the column has to be placed on the site boundary or closer to site boundary.
In this case,if we do not provide the stiffner beam how do we design the eccentric footing in first case?Also, how to design the second case eccentric footing?
Is it advisable to provide strap beam in eccentric footing and connect to the near by isolated footing? Please refer the attachment.
Kindly clarify which is the efficient method to design both case eccentric footing
Sathya.
 Filesize:  7.41 KB
 Viewed:  40 Time(s)
PostPosted: Sat Oct 26, 2019 4:21 am    Post subject: Reply with quote
You are welcome, Er. Sathya.... You have found the solution on your own ! Strap footing or Combined footing is the solution. Never attempt the proposals you had envisaged earlier, which is atrocious, at least theoretically !
PostPosted: Sat Oct 26, 2019 7:27 am    Post subject: Reply with quote
I wish to add that, in the 2nd case, you make a strap / combined footing by combining the column existing in the diagonal direction, if it is a must that the column has to rest on the corner of the footing..
sathyace
PostPosted: Sat Oct 26, 2019 10:32 am    Post subject: Reply with quote
Thank you sir,
Now clearly understood the concept.
Analysed the strap beam as simply supported beam, here i have attached the strap beam staad file for reference.
Kindly check and let me know if any corrections.
Thank you.
Sathya.
SB1.zip
 Filename:  SB1.zip
 Filesize:  672 Bytes
 Downloaded:  71 Time(s)
PostPosted: Sat Oct 26, 2019 2:52 pm    Post subject: Reply with quote
This is not the method to analyse Strap footings. You can refer books "Design of Reinforced Concrete Foundation" by Varghese (contains a number different cases / examples) or "Design of Reinforced Concrete Structures" by Gambhir, for guidance. If the distance of the column in question to the adjacent column is not much, you can better go for a combined footing.
sathyace
PostPosted: Thu Oct 31, 2019 1:38 pm    Post subject: Reply with quote
Thank you sir.I will refer those books.