IMPORTANT: SHEAR WALL RCDC
Arjun Jangid
PostPosted: Thu Feb 13, 2020 8:57 am    Post subject: IMPORTANT: SHEAR WALL RCDC Reply with quote
Greetings,
According to RCDC software, the calulation in shear wall is-
Interaction Principle (Discrete Action)
Moment capacity check
Ptcalculated= 0.52
Reinforcement required= 32-T12 + 12-T12
Load angle= Tan-1(Muy/Mux) = 14.95 deg
Corresponding NA angle (beta)= 87.72 deg
MRes= 548.01 knm
MCap= 2576.78 knm
Capacity ratio= MRes/MCap = 0.21<=1
I cannot figure out how beta value and MCap value is calculated.
As mentioned,
Beta= It is a Neutral Axis angle corresponding to load angle to find out MCap
MCap= Moment capacity of section for NA angle at design Pu
Please help for the same.
Thank you.
abhio
PostPosted: Wed Feb 26, 2020 7:53 am    Post subject: Reply with quote
Dear Er Jangid,
The analysis of a column (or shear wall) under axial load and biaxial bending moments is a trial-and-error procedure where the location and angle of the neutral axis are assumed and then iterated so as to equate externally applied load and bending moments to the summation of internal forces and moments of these forces.
There are a number of papers about this procedure. Brondum-Nielsen had a number of papers in "Concrete". Aristzalbal-Ochoa had one in ACI Structures Journal.
Arjun Jangid
PostPosted: Thu Feb 27, 2020 4:21 am    Post subject: Thank you! It was indeed very helpful. Reply with quote
abhio wrote:
Dear Er Jangid,