Location of Construction joints in continuous RCC Slab.
Goto page Previous  1, 2
 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1345
Location: Cochin

PostPosted: Sat Jul 07, 2012 10:39 am    Post subject: Reply with quote

Dear Engineers,

Suppose construction joint was provided to a beam at 1/3 to 1/4 span and the extension of the beam is carried out after one year only ( remaining 2/3 to 3/4 portion). Then how much bond will be achieved between old and new concrete ? What is the mechanism by which the bonding is achieved ? Will not there be a tendency for the joint to rift apart, the presence of reinforcement notwithstanding, even if the CJ is provided in the minimum BM / SF region as told above? What is the exact theory behind this ?

Regards,

E S Jayakumar
Back to top
View user's profile Send private message
thirumalaichettiar
Silver Sponsor
Silver Sponsor


Joined: 26 Jan 2003
Posts: 3544

PostPosted: Sat Jul 07, 2012 10:42 am    Post subject: Reply with quote

Er.Jeyakumar,
Pl.browse the link below in which I attached files clearing your doubt.

T.RangaRajan.
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 2212

PostPosted: Sat Jul 07, 2012 11:37 am    Post subject: Location of Construction joints in continuous RCC Slab. Reply with quote

We may have to distinguish between construction joint and stage construction

construction joint is the joint when concrete is still in its green stage and its treatment
before laying fresh concrete is prescribed in the IS codes.The time gap shall not be more
than 12-24 hrs or so ,i think.

Stage construction : This is generally terminated at support and dowel bars for taking
support BM as well as shear force are left in position for casting future slab in future.

If some seating is left on supporting wall/beam for future slab , then dowels for  
shear can be relieved. Otherwise dowels need to be left for both BM and shear
At time of future construction , old hardened concrete is roughened /brushed
and epoxy is applied prior to concreting , but shear as well as moment  
transfer is achieved thru dowels.


best regds

vikramjeet



Dear Engineers, Suppose construction joint was provided to a beam at 1/3 to 1/4 span and the extension of the beam is carried out after one year only ( remaining 2/3 to 3/4 portion). Then how much bond will be achieved between old and new concrete ? What is the mechanism by which the bonding is achieved ? Will not there be a tendency for the joint to rift apart, the presence of reinforcement notwithstanding, even if the CJ is provided in the minimum BM / SF region as told above? What is the exact theory behind this ? Regards, E S Jayakumar
-- ญญ

Posted via Email
Back to top
View user's profile Send private message
ajayapc
...
...


Joined: 14 Jul 2008
Posts: 64

PostPosted: Sun Jul 08, 2012 4:45 am    Post subject: Location of Construction joints in continuous RCC Slab. Reply with quote

Dear Sefians,In continuation to earlier comments, the joints shall be along perpendicular direction to the main reinforcement in slab and shall be located at 0.24 - 0.33 L (where L= span of slab in short direction), the location where SF ~ 0.
Regds



Ajay C



On Sat, 7/7/12, vikram.jeet <forum@sefindia.org> wrote:
Quote:

From: vikram.jeet <forum@sefindia.org>
Subject: [SEFI] Re: Location of Construction joints in continuous RCC Slab.
To: general@sefindia.org
Date: Saturday, 7 July, 2012, 7:17 PM

           We may have to distinguish between construction joint and stage construction

construction joint is the joint when concrete is still in its green stage and its treatment
before laying fresh concrete is prescribed in the IS codes.The time gap shall not be more
than 12-24 hrs or so ,i think.

Stage construction : This is generally terminated at support and dowel bars for taking
support BM as well as shear force are left in position for casting future slab in future.

If some seating is left on supporting wall/beam for future slab , then dowels for
shear can be relieved. Otherwise dowels need to be left for both BM and shear
At time of future construction , old hardened concrete is roughened /brushed
and epoxy is applied prior to concreting , but shear as well as moment
transfer is achieved thru dowels.


best regds

vikramjeet



Dear Engineers, Suppose construction joint was provided to a beam at 1/3 to 1/4 span and the extension of the beam is carried out after one year only ( remaining 2/3 to 3/4 portion). Then how much bond will be achieved between old and new concrete ? What is the mechanism by which the bonding is achieved ? Will not there be a tendency for the joint to rift apart, the presence of reinforcement notwithstanding, even if the CJ is provided in the minimum BM / SF region as told above? What is the exact theory behind this ? Regards, E S Jayakumar
-- ญญ
     



     




Posted via Email
Back to top
View user's profile Send private message
aslrah
SEFI Member
SEFI Member


Joined: 01 Oct 2008
Posts: 18

PostPosted: Wed Mar 16, 2016 5:43 am    Post subject: construction joint Reply with quote

Should the main bars be terminated at construction joint or they can continue as per the design for whole slab. Thanks for the reply.
Back to top
View user's profile Send private message
sknsrinivasan
...
...


Joined: 15 Apr 2013
Posts: 281

PostPosted: Wed Mar 16, 2016 6:16 am    Post subject: Re: construction joint Reply with quote

Dear aslrah

  The main Bar should continue at construction joint. Why we are providing construction joint we cant pouring the concrete at same time since incompletion of shuttering work and steel fabrication. you should provide construction joint 1/3 of span from the support This is as far as my knowledge

  In PT area Not like this because the Tendon  stressing portion will be at construction joint area. we have to provide additional reinforcement in construction joint area. i dont know how that reinforcement given by PT vendor  

Regards
N.Srinivasan
  

aslrah wrote:
Should the main bars be terminated at construction joint or they can continue as per the design for whole slab. Thanks for the reply.
Back to top
View user's profile Send private message
mishelwilson28
SEFI Member
SEFI Member


Joined: 26 Jun 2020
Posts: 1

PostPosted: Fri Jun 26, 2020 6:13 pm    Post subject: Reply with quote

Hello there,

Can you please tell me which is company provides good contraction services? Because I'm purchasing a new home but I don't have an idea where to go to find good contraction group company you have any idea so please discuss to me.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy