RCC BEAM FOR 15M SPAN

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
Ashik L Keremane
SEFI Member
SEFI Member


Joined: 07 Apr 2020
Posts: 6

PostPosted: Sun Sep 13, 2020 6:56 am    Post subject: RCC BEAM FOR 15M SPAN Reply with quote

Good Noon SEFI members,

Is it possible to design an RCC beam for 15m span? I tried to design , I took depth of 1.125m. Is it enough or is there any other special consideration to take care?

If not RCC beam, is it possible to go for waffle slab?

If both are possible, which is cost effective. Long span RCC beam or Waffle Slab?

Please help!!
Back to top
View user's profile Send private message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1360
Location: Cochin

PostPosted: Tue Sep 15, 2020 1:09 pm    Post subject: Reply with quote

It is possible. We have done a beam of span 17.5m for the balcony of a community hall (shown in the picture). You can check the deflection of the beam by the criteria given in Cl: 23.2 & 24.1 of IS 456 : 2000. The attached Spreadsheet will be helpful for this. Also, you can provide slight upward camber for the beam, to counter the possible deflection.

E S Jayakumar



Long beam.jpg
 Description:
 Filesize:  68.96 KB
 Viewed:  24 Time(s)

Long beam.jpg



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
DESIGN OF SLABS & SINGLY REINFORCED BEAMS.xls
 Description:

Download
 Filename:  DESIGN OF SLABS & SINGLY REINFORCED BEAMS.xls
 Filesize:  47 KB
 Downloaded:  88 Time(s)

Back to top
View user's profile Send private message
Ashik L Keremane
SEFI Member
SEFI Member


Joined: 07 Apr 2020
Posts: 6

PostPosted: Tue Sep 15, 2020 1:16 pm    Post subject: Reply with quote

es_jayakumar wrote:
It is possible. We have done a beam of span 17.5m for the balcony of a community hall (shown in the picture). You can check the deflection of the beam by the criteria given in Cl: 23.2 & 24.1 of IS 456 : 2000. The attached Spreadsheet will be helpful for this. Also, you can provide slight upward camber for the beam, to counter the possible deflection.

E S Jayakumar


Thank you for sharing the information. May i know what is the depth of beam provided here?
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy