Dear sir,
In staad pro, load combination we add 1.5 for DL and LL (1.5DL+1.5LL) and design of footing the load on footing is axial load on individual column /1.5 or  individual column /3 which is correct.
Somebody says divide by 3 because we add 1.5 for both DL and LL
G.Velrajkumar
 Filesize:  169.48 KB
 Viewed:  133 Time(s)
PostPosted: Sun Jun 27, 2021 3:50 pm    Post subject: Reply with quote
Foundation design:
In staad , the input on loading combination is :
1.5*DL + 1.5*LL
For comparing base pressures underneath footing ,  the  Factored Column load shall be divided by 1.5 to arrive at working Load on column footing . Base pressures must be worked out for. Working load without any load factor.