Slab thickness
Goto page Previous  1, 2
 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3839

PostPosted: Mon Aug 08, 2022 1:25 pm    Post subject: Reply with quote

Er Ramu

Calculations for deflection  Chek purposes:

As per calcs fm u , pt = 0.128 for LF =1.0

Refer to chart figure 3 , the multiplier is 2.0

The effect of continuity cannot be taken twice , the % reinforcement worked is based on continuity and there fore Gross value of L/d = 2*20= 40

Hence eff depth = 327/40 = 8.2cm
Overall depth = 8.2+ 2= 10.2 cm  cf 11.5   ok  - - - This is as per clause 22.2.1

Also as per clause 23.1 for slabs as already discussed , L/D = 32
Hence D , the o/all depth = 327/32 = 10.22 cm , just the same

Calculation for reinf provision :
Actual reinf to be provided based on LF= 1.5
Hence Mu/bd^2 = 0.426*1.5 = 0.639 pt = 0.187
Ast 0.187*9.5= 1.78 cm2/m
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3839

PostPosted: Mon Aug 08, 2022 3:10 pm    Post subject: Reply with quote

One thing must be borne in mind that while making deflection check using load factor = 1.0 , pl calculate pt and see modification factor and do not further calculate Ast , Since Ast to be provided has to be based on Pt using  Load factor =1.5.

Just my view after seeing yr calcls
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3839

PostPosted: Mon Aug 08, 2022 3:28 pm    Post subject: Reply with quote

Er Ramu

Cantilever slab

Your calcs are OK and depth rightly revised . Cantilever slabs must be provided with liberal depth as reinf is at top and chances of reinf getting little down at site are very much there inspite of placing chairs precautions  . Even some designers always take view of this and provide some additional reinf at Cantilever slabs , though many designers who are very rigid may not encourage this . But while providing we have to judge site situations and should not act as theoretical  tigers.
Back to top
View user's profile Send private message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 110

PostPosted: Mon Aug 08, 2022 4:22 pm    Post subject: Reply with quote

Thank you sir for giving such a brief explanation.

Why do we have to use the load factor as 1 for % of reinforcement calculation to find out the modification factor?

Is there any specfic codal provison for this?

To calculate fs we need to know Ast required and Ast provided, so this Ast is based on load factor 1 or load factor 1.5?

Thanks & Regards,
Ramu.
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3839

PostPosted: Tue Aug 09, 2022 3:24 am    Post subject: Reply with quote

Deflection is serviceability requirement and as per IS 456 this needs to be checked at working loads as evident from  clause 35.4 on partial safety factors for Loads Table 12  ( relating clauses 18.3 and 35.4.1 of IS 456 1978).

The Load factor for serviceability limits is( 1.0 DL + 1.0 LL)
Back to top
View user's profile Send private message
spsvasan
...
...


Joined: 18 Dec 2008
Posts: 382

PostPosted: Sun Aug 14, 2022 10:11 am    Post subject: Reply with quote

Dear Er.Ramu & Er.Vikramjeet

I am generally in agreement with Er.Vikramjeet. However, I differ in one aspect only

fs = 0.58 x fy x  Ast(required) / Ast(provided)
fs = 0.58 x 415 x 122 / 250 = 117.46 N/mm2
As per Fig.4 in IS-456:2000
M.F = 2.0


In the above calculation IMHO, Ast (required) is to be the limit state requirement only, ie 178 sqmm/m.

In the expression fs = 0.58 fy (As reqd / As provided), the factor 0.58 lowers the limit state stress to the service stage level

In this particular case, the modification factor still remains as 2.0

S.P.Srinivasan
Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3839

PostPosted: Mon Aug 15, 2022 3:27 pm    Post subject: Reply with quote

spsvasan wrote:
Dear Er.Ramu & Er.Vikramjeet

I am generally in agreement with Er.Vikramjeet. However, I differ in one aspect only

fs = 0.58 x fy x  Ast(required) / Ast(provided)
fs = 0.58 x 415 x 122 / 250 = 117.46 N/mm2
As per Fig.4 in IS-456:2000
M.F = 2.0


In the above calculation IMHO, Ast (required) is to be the limit state requirement only, ie 178 sqmm/m.

In the expression fs = 0.58 fy (As reqd / As provided), the factor 0.58 lowers the limit state stress to the service stage level

In this particular case, the modification factor still remains as 2.0

S.P.Srinivasan


Yes ,  In case stress is calculated instead of reinf % pt at LF=1.0 ,   factor fs  be based as   rightly expressed by Er SP Srinivasan.
Back to top
View user's profile Send private message
BVRAO
General Sponsor
General Sponsor


Joined: 21 Sep 2009
Posts: 50

PostPosted: Tue Aug 16, 2022 1:03 pm    Post subject: Reply with quote

Slab Design with deflection check


Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
2WaySlabDesign.rar
 Description:
Slab Design with deflection check

Download
 Filename:  2WaySlabDesign.rar
 Filesize:  42.41 KB
 Downloaded:  124 Time(s)

Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy