smtenr SEFI Member

Joined: 23 Jan 2012 Posts: 4
|
Posted: Sat Dec 10, 2022 8:20 am Post subject: Wind load calculation for pyramid shape space structure |
|
|
Dear members,
I am designing a pyramid shape space frame structure,
For wind load calculation which clause and table shall I use for pressure coefficient from IS875 Part3
Ashish |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3714
|
Posted: Sun Dec 11, 2022 9:36 am Post subject: |
|
|
Pyramid type str :
Since pyramid str cladding is wall as well as roof
External pr coeffs - Higher effects to be taken by working out from - - table 5 values on projected vertical area and Table 6 values on projected plan atea ,, I think .
Hope some other members may further clarify.
Internal pr coff - ( + & - )O. 2p /O.5p /O.7pas per opening% |
|
Back to top |
|
 |
smtenr SEFI Member

Joined: 23 Jan 2012 Posts: 4
|
Posted: Mon Dec 12, 2022 2:42 am Post subject: Wind load calculation for pyramid space frame |
|
|
vikram.jeet wrote: | Pyramid type str :
Since pyramid str cladding is wall as well as roof
External pr coeffs - Higher effects to be taken by working out from - - table 5 values on projected vertical area and Table 6 values on projected plan atea ,, I think .
Hope some other members may further clarify.
Internal pr coff - ( + & - )O. 2p /O.5p /O.7pas per opening% |
Thank you , Vikram sir,
As it is a open structure with no wall and cladding
I internal press. Coefficient. +/-0.7 , I used
Thanks for guiding me on ext. Pressure coefficient.
Ashish |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3714
|
Posted: Wed Dec 14, 2022 2:46 am Post subject: |
|
|
vikram.jeet wrote: | Pyramid type str :
Since pyramid str cladding is wall as well as roof
External pr coeffs - Higher effects to be taken by working out from - - table 5 values on projected vertical area and Table 6 values on projected plan atea ,, I think .
Hope some other members may further clarify.
Internal pr coff - ( + & - )O. 2p /O.5p /O.7pas per opening% |
CORRECTION IN ABOVE POST :
EXTERNAL PR COEFFICIENT - TO BE TAKEN CUMULATIVE EFFECT OF TABLE 5 ON PROJECTED VERTICAL AREA + TABLE 6 PROJECTED PLAN AREA
SORRY FOR INCONVENIENCE |
|