Reinforcemnt in bridge abutment base
paudel257
PostPosted: Mon Mar 18, 2024 5:12 am    Post subject: Reinforcemnt in bridge abutment base Reply with quote
Can anybody suggest me about providing distribution reinforcemnt in the base of attached bridge abutment highlited portion
bridge_abutment.pdf
 Filename:  bridge_abutment.pdf
 Filesize:  32.59 KB
 Downloaded:  55 Time(s)
PostPosted: Thu Mar 21, 2024 3:34 am    Post subject: Reply with quote
The abutment sketch not clear,  presume base slab with counterfort stem .
Distribution steel from consideration of shrinkage /temp shall be min 0.12 percent ,, if treated as base slab ,
However in bridges,, distribution to extent of  (0.2* Main DLM + 0.3* Main LLM)  is generally taken in deck slabs and same criterion could be applied  ,,
But if abutment is mass conc abutment ,, surface reinforcement as per IRC 78 can only be suffice.
spsvasan
PostPosted: Sun Mar 24, 2024 12:13 pm    Post subject: Re: Reinforcemnt in bridge abutment base Reply with quote
I generally agree with Er.Vikramjeet. Only, the use of 0.2 DLBM + 0.3 LLBM will not be necessary
Does the black inclined line  indicate counterforts
Usually, in abutments, the heel is long and toe is short to ensure better stability
S.P.Srinivasan