TORSIONAL IRREGULARITIES

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
LELE AND ASSOCIATES
...
...


Joined: 17 Apr 2010
Posts: 130

PostPosted: Wed May 08, 2024 6:15 am    Post subject: TORSIONAL IRREGULARITIES Reply with quote

Hello,


I am working on a residential building project the model of which is attached herewith.
While checking the seismic parameters for irregularities, there are warnings that the building has torsional irregularity. It is not possible always to have the building planned in such a way that the structure has no torsional irregularity. My question is, how do we correct this irregularity in the case of the attached model?

Thank you
Prashant.



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
SDVTR3.rar
 Description:

Download
 Filename:  SDVTR3.rar
 Filesize:  41.58 KB
 Downloaded:  192 Time(s)

Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3917

PostPosted: Thu May 09, 2024 4:29 am    Post subject: Reply with quote

Warnings in output :-

I am not any expert on cadd,  but I think these warning can be tackled by providing horizontal spring supports at two locations in plan,, but with very very little spring value,, I. e though it is support but with negligible resistance,, more to satisfy software 's inherent requirements..
Not sure but one can try,,
Back to top
View user's profile Send private message
sakumar79
...
...


Joined: 18 Apr 2008
Posts: 716

PostPosted: Thu May 16, 2024 1:34 am    Post subject: Reply with quote

Dear Sir,
    In one of my projects where there was torsional irregularity, I had to resolve it by playing with column sizes to get the correct side stiff enough to prevent the twisting. Also,
a. Column size cannot be 230 mm when you are doing ductile detailing.
b. I would not recommend having change in column size over the floors.
c. Check if you can avoid the shear wall completely. That may be the reason for the torsional irregularity.
d. Why is there RC wall in lowest level only in one portion?

Hope that helps,
S Arunkumar
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy