A COMPREHENSIVE REVIEW OF ULTRASONIC PULSE VELOCITY TESTING.

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
P.K.Mallick
General Sponsor
General Sponsor


Joined: 14 Dec 2008
Posts: 1111

PostPosted: Sun Apr 28, 2024 9:32 am    Post subject: A COMPREHENSIVE REVIEW OF ULTRASONIC PULSE VELOCITY TESTING. Reply with quote

A COMPREHENSIVE REVIEW OF ULTRASONIC PULSE VELOCITY TESTING.
Introduction: The Ultrasonic Pulse Velocity method is truly a non-destructive method resulting in no damage to the Concrete element being tested. This method makes use of Mechanical Waves. A test specimen in a particular location can be tested multiple times using this method, which helps in monitoring concrete undergoing internal structural changes over a long period of time. This method can be used for detecting internal cracking and other defects as well as changes in Concrete such as deterioration due to aggressive chemical environment, freezing and thawing. This method can also be used to estimate strength of concrete test specimens and in-place concrete.
Principle: Three types of propagating mechanical waves, also called Stress Waves, are created when surface of an elastic medium is disturbed by a dynamic or vibratory load. There are three types of propagating mechanical waves:
1)     Compressional Waves also known as Longitudinal or P-waves.
2)     Shear Waves also called Transverse or S-Waves.
3)     Surface Waves also called Rayleigh Waves.
The compressional waves propagate through the solid medium in a fashion analogous to sound waves propagating through air. Each wave type propagates with its characteristic velocity. For a given solid, compressional waves have highest velocity and surface waves the lowest and therefore, compressional wave is received fast by the transducer. The velocity of pulses is almost independent of the geometry of the material through which they pass but it depends on only elastic properties of the material through which they pass. Therefore, the pulse velocity method is an useful technique for investigating in-situ concrete because comparatively higher velocities are obtained when the quality of concrete in terms of density, homogeneity and uniformity is good. In case of poorer quality, lower velocities are obtained. The crack, void or flaws in the concrete come in the way of transmission of pulses, and then the pulses pass around the discontinuity resulting in the longer transmission path, consequently lower velocity. The actual pulse velocity obtained depends primarily upon the materials and mix proportions of concrete and density. The modulus of elasticity of aggregate also significantly affects the pulse velocity. For the Concrete, the value of pulse velocity typically ranges from 3000 to 5000 m/s.
Apparatus: As per IS: 516(Part-5/Sec: 1):2018, Ultrasonic Pulse Velocity Testing, the apparatus for Ultrasonic Pulse Velocity measurement shall consist of the following:
1)     Electrical Pulse generator.
2)     Transducers- One pair.
3)     Standard Calibration Bar.
4)     Amplifier.
5)     Electronic Timing Device.  
Piezoelectric and magneto-strictive type of transducers may be used, but magneto-strictive type is more suitable for the lower part of the frequency range. High frequency pulses have a well-defined onset but as they pass through the concrete, they become attenuated more rapidly than pulses of lower frequency. It is preferable to use high frequency transducers (60 KHZ to 200 KHZ) for short path length of around 50mm. The low frequency transducers (10 KHZ to 40 KHZ) are for long path length up to 15m (Maximum). Transducers with a frequency of 25KHZ to 100KHZ are found to be useful for most applications. The apparatus shall be capable of measuring transit times to an accuracy of ±1 percent over a range of 20 microseconds to 10 milliseconds.
Determination of Pulse Velocity: The basic idea on which the pulse velocity method is established is that the velocity of a pulse of compressional waves through a medium depends on the elastic properties and density of the medium.



Fig-1: Pulse Velocity Instrument (Ref: 3)


Fig: 2: Schematic Diagram of Pulse Velocity Test Circuit (Ref: 3)
The transmitting transducer of the pulse velocity instrument transmits a wave into the concrete and the receiving transducer, at a distance L, receives the pulse through the concrete at another point. The pulse velocity instrument “DISPLAY” indicates the transit time “T”, it takes for the compressional wave pulse to travel through the concrete. The compressional wave pulse velocity “V”, therefore is V=L/T. The compressional pulse transmitted through the concrete undergoes scattering at various aggregate mortar boundaries. By the time the pulse reaches the receiving transducer, it becomes transformed into a complex wave form, which contains multiply reflected compressional waves and shear waves. Of course, compression waves travelling the fastest arrive first at the receiver.
Precautions to be taken during Test: To transmit or to receive the pulse, the transducer must be in full contact with test object. Otherwise an air pocket between the test object and transducer may introduce an error in the indicated transit time. This error is introduced because only a negligible amount of wave energy can be transmitted through air. There are many couplants available in the market, the use of which eliminates air pockets. Those couplants are Petroleum jelly, Grease, Liquid Soap and Kaolin-glycerol paste. The couplant layer should be as thin as possible. While applying constant pressure on the transducers, repeated reading at a particular location should be taken until a minimum value of transit time is obtained. If the concrete surface is very rough, thick grease should be used as couplant. In some cases, the rough surface may have to be grounded smooth or a smooth surface may have to be established with the use of plaster of paris or suitable quick-setting cement paste or quick setting epoxy mortar.
Transducers arrangement: When two transducers are placed on opposite faces of the specimen, the maximum energy is propagated and it is called “DIRECT TRANSMISSION”. When two transducers are placed on adjacent faces, it is called “SEMI-DIRECT TRANSMISSION”. When two transducers are placed on the same face, it is called “INDIRECT OR SURFACE TRANSMISSION”.
  
     
Fig: 3: Positioning of Transducers {Ref: 1)
The indirect transmission arrangement is the least sensitive and is used when only one face of the concrete is accessible or when the quality of the surface concrete relative to the overall quality is of interest. The semi-direct transmission arrangement is used when the direct arrangement cannot be used, for example at the corners of structures.
The above three methods have been defined in IS: 516 (Part 5/ Sec 1} 2018, Ultrasonic Pulse Velocity Testing. But in addition to above, BS EN 12504-4, 2021, Determination of Ultrasonic Pulse Velocity Test (British Standard) describes another method which is called “PULSE-ECHO TRANSMISSION”. This method like indirect transmission is used only when single face of the specimen is available. But this method uses only one transducer both for transmitting and receiving. In this case of Pulse-Echo transmission, the receiver detects pulses which have travelled through the concrete to the opposite surface and have been reflected back to the first surface. The sensitivity of this test is comparable with “Direct Transmission”.
Path Length Measurements: For direct transmission, the path length is the shortest distance between the transducers. The measurement of the path length shall be recorded to the nearest 1 percent of the measured distance. For semi-direct transmission, it is generally found to be sufficiently accurate to take the path length as the distance measured from center to center of the transducer faces. The accuracy of path length is dependent upon the size of the transducer compared with the center to center distance. With indirect transmission, the path length is not measured but a series of measurements is made with the transducers at different distance apart. For Pulse-Echo transmission the path length is two times the distance from the surface where the transducer is placed and the opposite surface. The path length shall be recorded as per the direct transmission. Since size of aggregates influences the pulse velocity measurement, it is recommended that for direct transmission method, the minimum path length shall be 100mm for concrete in which the nominal maximum size of aggregate is 20mm or less and 150mm for concrete in which the nominal maximum size of aggregate is between 20mm and 40 mm.
Interpretation of Results: The Ultrasonic Pulse Velocity of concrete depends on the materials and mix proportions used in the making concrete as well as method of placing, compaction and curing of concrete. If the concrete is not compacted as thoroughly as possible, or if there is segregation of concrete during the placing or there are internal cracks or flaws, the pulse velocity will be lower, although the same materials and mix proportions are used. The quality of concrete in terms of uniformity, incidence or absence of internal flaws, cracks and segregation, etc. (indicative of the level of workmanship employed) can be assessed using the guidelines given in Table-1, taken from first amendment of IS: 516 (Part 5/ Sec 1} 2018, Ultrasonic Pulse Velocity Testing. This table is only for concrete quality grading and shall not be used for estimating concrete grades from Ultrasonic Pulse Velocity values. When comparison is made based on Table-1 amongst different parts of a structure, which have been built at the same time with supposedly similar materials, construction practice and supervision, the assessment of quality becomes more meaningful and reliable. When the UPV values are lesser by more than 10 percent of average value of the member/part of structure, the location shall be considered as having internal flaws or segregation caused by poor workmanship or there could be micro cracks.  





Determination of pulse velocity-Indirect Transmission: With indirect transmission, there is some uncertainty regarding the exact length of the transmission path because of the significant size of the areas of contact between the transducers and the concrete. It is preferable to make a series of measurements with transducers at different distances apart to eliminate this uncertainty. To do this, the transmitting transducer shall be placed in contract with concrete surface at a fixed point and the receiving transducers shall be placed at fixed increments Xn along a chosen line on the surface. The transmission times recorded shall be plotted as points on a graph showing their relation to the distance separating the transducers. The slope of the best straight line drawn through the point (1/tanØ) shall be measured and recorded as the mean pulse velocity along the selected line on the concrete surface where the points measured and recorded in this way indicate a discontinuity, it is likely that a surface crack or surface layer of inferior quality is present and a velocity measured in such an instance is unreliable.

Figure-4: Example of determination of Pulse Velocity by Indirect (Surface) transmission (Ref-2)
R= Receiver Transducer.
T= Transmitter Transducer.
t = Transit Time.
X1= Distance between transmitter and receiver transducer.
As per IS: 516 (Part 5/Sec-1): 2018, Ultrasonic Pulse Velocity Testing, surface probing in general gives lower pulse velocity than in case of cross probing and depending on number of parameters, the difference could be of the order of about 0.5 Km/s. In view of this, it is recommended that in surface probing method the pulse velocity may be increased by 0.5 Km/s, for values ≥ 3.0 Km/s.
Correlation of Pulse Velocity and Compressive Strength: The assessment of compressive strength of concrete from Ultrasonic Pulse Velocity values is not adequate because the statistical confidence of the correlation between Ultrasonic Pulse Velocity and Compressive Strength of Concrete is not high. This is because large numbers of parameters are involved which influence the pulse velocity and compressive strength of concrete to different extent. However, if actual concrete materials and mix proportions adopted in a particular structure are available, then estimate of Concrete Strength can be made by establishing suitable correlation between the Pulse Velocity and the Compressive Strength of concrete specimens made with such materials and mix proportions, under the environmental conditions similar to the structure. The estimated strength may vary from the actual strength by ±20 percent. The correlation so obtained may not be applicable for concrete of another grade or made with different types of materials. If correlation graph is not available, but the velocities on concrete cubes are available, the average pulse velocity in members of structures are not expected to deviate more than 10 to 15 percent of Pulse velocity values obtained on concrete cubes(Dry Surface).
Other uses of Ultrasonic Pulse Velocity Testing:    As per IS: 516 (Part 5/Sec-1): 2018, Ultrasonic Pulse Velocity Testing, this testing can be used:
1)     For estimating the depth of a surface crack.
2)     For determining the dynamic young’s Modulus of Elasticity(E) of the concrete.
Factors influencing Pulse Velocity Measurements:
1)     Surface Condition and moisture content of concrete.
2)     Path length, Shape and Size of Concrete member.
3)      Temperature of Concrete.
4)     Influence of Stress.
5)     Effect of Reinforcement.
6)     Contract between Transducer and Concrete.
7)     Cracks and voids.
Point of Discussion: As per IS: 516 (Part 5/Sec-1): 2018, Ultrasonic Pulse Velocity Testing, concrete quality grading has been divided into three categories:
1)     Excellent
2)     Good
3)     Doubtful.
The code says that in case of “Doubtful Quality”, it shall be necessary to carry out additional tests.
From the above, can it be inferred that the concrete quality grading of “Excellent” and “Good” may not require any structural intervention and attention shall be paid only to Concrete Quality Grading of “Doubtful Category”?
References:
1)     IS: 516 (Part 5/Sec1):2018, Hardened Concrete-Method of Test, Part (5) Nondestructive Testing of Concrete, Section-1, Ultrasonic Pulse Velocity Testing with Amendment-1.
2)     BS EN 12504-4:2021 Testing Concrete in Structures, Part 4: Determination of Ultrasonic Pulse Velocity.
3)     Handbook of Nondestructive Testing of Concrete edited by V.M.Malhotra and N.J.Carino.



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
ULTRASONIC PULSE VELOCITY TESTING.pdf
 Description:

Download
 Filename:  ULTRASONIC PULSE VELOCITY TESTING.pdf
 Filesize:  870.21 KB
 Downloaded:  486 Time(s)


_________________
P.K.Mallick
p.k.mallick1962@gmail.com
9472967626


Last edited by P.K.Mallick on Mon Apr 29, 2024 7:21 am; edited 12 times in total
Back to top
View user's profile Send private message
alpa_sheth
...
...


Joined: 26 Jan 2003
Posts: 305

PostPosted: Tue May 28, 2024 6:12 am    Post subject: Reply with quote

Thank you Mallick ji for a comprehensive review on Pulse Velocity Testing. The document is exhaustive. I would like if you could share some wisdom on the use of UPV for estimating the Concrete strength from UPV. I ask this because I normally use it for checking the integrity and quality  of the concrete, but I have seen some using it for strength estimation purpose.
How reliable would it be to estimate the strength?

On another note could you, or any expert on the Forum throw some light on the Concrete strength results from concrete drilled core tests. I have seen a variance of more then 60%  in drilled core test results of columns taken from concrete of a single batch. Preparation of the concrete core prior to testing plays a crucial role and what is the best method for this? Grinding the top or capping with cement mortar?

I have found that often the cores fail due to improper preparation of the core end.

Best regards,
Alpa Sheth
Back to top
View user's profile Send private message
P.K.Mallick
General Sponsor
General Sponsor


Joined: 14 Dec 2008
Posts: 1111

PostPosted: Tue May 28, 2024 6:31 am    Post subject: Reply with quote

Madam,
I will come back on 1st issue. I need some time.
Regarding 2nd issue on the Core Test, I have posted a write-up in Sefi recently. Please have a look at that. In the comment section of that write-up, I will write about Capping and grinding.





alpa_sheth wrote:
Thank you Mallick ji for a comprehensive review on Pulse Velocity Testing. The document is exhaustive. I would like if you could share some wisdom on the use of UPV for estimating the Concrete strength from UPV. I ask this because I normally use it for checking the integrity and quality  of the concrete, but I have seen some using it for strength estimation purpose.
How reliable would it be to estimate the strength?

On another note could you, or any expert on the Forum throw some light on the Concrete strength results from concrete drilled core tests. I have seen a variance of more then 60%  in drilled core test results of columns taken from concrete of a single batch. Preparation of the concrete core prior to testing plays a crucial role and what is the best method for this? Grinding the top or capping with cement mortar?

I have found that often the cores fail due to improper preparation of the core end.

Best regards,
Alpa Sheth

_________________
P.K.Mallick
p.k.mallick1962@gmail.com
9472967626
Back to top
View user's profile Send private message
P.K.Mallick
General Sponsor
General Sponsor


Joined: 14 Dec 2008
Posts: 1111

PostPosted: Thu May 30, 2024 8:46 am    Post subject: Reply with quote

USE OF UPV FOR ESTIMATING THE CONCRETE STRENGTH.
Stipulations of IS: 516 (Part 5/Sec1) have already been stated in the body of above write-up. (Kindly see the heading in Bold- “Correlation between Pulse Velocity and Compressive Strength”). Therefore, let us, now, explore what are the options available in other publications.
1)     Provisions in ACI 228.1R-03, In-place Methods to Estimate Concrete Strength, Reported by ACI Committee 228.
This publication starts with basic premises that the Pulse Velocity is proportional to square root of Elastic Modulus. Because the Elastic Modulus and strength of a given concrete increase with maturity, it follows that Pulse Velocity may provide a means of estimating strength of Concrete, even though there is no physical relationship between these two properties. As Concrete matures, however, the elastic modulus and compressive strength increase at different rates. At early maturities, the elastic modulus increases at a higher rate than strength, and at later maturities, the Elastic Modulus increases at a lower rate. As a result, over wide range of maturity, the relationship between Compressive Strength and Pulse Velocity is highly Non-linear. Further, ACI 228-1R-03 has provided a figure showing a typical relationship between Compressive Strength and Pulse Velocity, stating that it is only an illustrative example and the actual relationship depends on the specific Concrete mixture.
The code concludes by stating that Pulse Velocity con be used to estimate strength in new and existing structure.

Fig-A Schematic of typical relationship between Pulse Velocity and Compressive Strength of a given Concrete mixture. (Ref: ACI 228.1R-03)

2)     Provisions in ASTM, C597-22, Standard Test Method for Ultrasonic Pulse Velocity through Concrete.
This publication states that if circumstances warrant a Velocity-Strength relationship may be established by the determination of Ultra Sonic Pulse velocity and Compressive Strength on a number of specimens of a concrete. This relationship may serve as a basis for the estimation of strength by further pulse velocity tests on that Concrete. It is further stated to refer ACI: 228.1R4 for guidance on procedure for developing and using such a relationship.
3)     Provisions in the article “The Ultrasonic Pulse Velocity Method by Tarun R. Naik, V.Mohan Malhotra and John S. Popovics published in HANDBOOK ON NONDESTRUCTIVE TESTING OF CONCRETE edited by V.M.Malhotra and N.J.Carino.
The above article states that the Pulse Velocity method may provide a means of estimating the strength of both in-situ and precast concrete although there is no physical relation between strength and velocity. The strength can be estimated from the Pulse Velocity by a pre-established graphical correlation between the two parameters. A figure has been provided there to as an example.

Fig-B Example Strength vs. Velocity relationship for estimation of Strength of Concrete.
This publication also talks about an article naming “Development of Statistical Quality Assurance Criterion for Concrete using Ultrasonic Pulse Velocity Method by K.K.Phoon, T.H.Wee, and C.S. Loi published in ACI Materials Journal/ September-October 1999. (This article is attached for reference.) This article proposes, including a worked out example, a probabilistic model to predict compressive strength from Ultrasonic Pulse Velocity.
4)     Provisions in book by A.M. Neville, Properties of Concrete.
This publication states that no unique relation between Ultrasonic Pulse Velocity and Compressive Strength exists. It further states that the Ultrasonic Wave Velocity is related to the density of Concrete. This relation offers rationale for the use of the ultrasonic wave velocity measurements for the purpose of assessing the strength of concrete, but subjected to strict limitations viz changes in hardness of cement paste, change in water/cement ratio, moisture condition of concrete, presence of reinforcement, etc. This publication provides two important figures. The first figure is about relation between compressive strength and ultrasonic pulse velocity for hardened cement, mortar and concrete in dry and moist condition, which is taken from ACI SP-82.
The second figure provides curves for assessment of the in-situ compressive strength of concrete using the combined ultrasonic pulse velocity and rebound hammer tests.









Fig-C Relation between Compressive Strength and Ultrasonic Pulse Velocity for hardened Cement paste, mortar and Concrete in dry and moist condition.







Fig-D Curves for assessment of in-situ Compressive Strength of Concrete using the combined Ultrasonic Pulse Velocity and Rebound Hammer Tests.



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
Development of Statistical Quality Assurance Criterion for Concrete Using Ultasonic Pulse Velocity Method.pdf
 Description:

Download
 Filename:  Development of Statistical Quality Assurance Criterion for Concrete Using Ultasonic Pulse Velocity Method.pdf
 Filesize:  88.89 KB
 Downloaded:  230 Time(s)


_________________
P.K.Mallick
p.k.mallick1962@gmail.com
9472967626
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy