flat slab span arrangement and design technique

 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conferences-2008 [ Flat Slab Design issues ]
View previous topic :: View next topic  
Author Message
k.gangadharan
General Sponsor
General Sponsor


Joined: 01 Apr 2008
Posts: 204

PostPosted: Mon Dec 22, 2008 2:51 pm    Post subject: flat slab span arrangement and design technique Reply with quote

I have one point to make clear from the experts on Flat slabs.In the
direct design method of flat slab design, one must have  at least
three spans in each plan directions But in  the equivalent frame
method this stipulation is not a must. Some architects make plans with
2 large spans and two cantilevers on both sides of the spans and in
some cases with a single span and two cantilevers and they want
structural design to be carried out with flat slab or flat plate.In
such cases, is it advisable to go for flat slab or flat plate design
for a building of 20 floors and more in an earth quake zone.Of course
these buildings have shear walls all around the  lift core.For doing
the analysis of these buildings can we go for finite element analysis
with rigid diaphragm assumptions for the slabs?.In a previous
discussion in sefi forum about flat slabs some members were expressing
to assume 75% of the lateral loads to be taken by the shear walls and
the balance 25% by the available columns. I wish to know how this
apportionment is possible in the program input if we are analysing by
STAAD or ETABS. Please clarify this?.

regards
K.Gangadharan  (assekg
Trivandrum

Posted via Email
Back to top
View user's profile Send private message
dipakdgaikwad
...
...


Joined: 01 Apr 2008
Posts: 77
Location: Mumbai

PostPosted: Tue Dec 23, 2008 7:35 am    Post subject: flat slab span arrangement and design technique Reply with quote

Dear K.Gangadharan
                  I am trying to answer second part of your query which is related to how to satisfy the clause of (25% +75%) base shear distribution using STAAD.Please note that this distribution is for dual system and not for Flatslab+Corewall type building. You can do this by three methods explained bellow.

                 1. Run the analysis checks the % bases shear taken by Frame. If it is less than 25 %.Calculate the scale factor such that after multiplying base shear contribution by frame will become 25%.Rerun the analysis using this scale factor.

                 2.If you are using plate element for shear wall modeling you can change thickness of plate element such way that frame will take at least 25 % base shear. Off course you have to attempt no of trials for this..
                 3. One more option is by defining different load combinations.
For this one has to calculate scale factor as explained in method 1 and has to define separate load combination by modifying basic load combination and by using load list command design frame elements for this combination.
E.g. suppose you workout scale factor 1.25 then the load combination 1.5(DL+EQ) will become 1.5DL+1.875EQ.
     Dear expert please correct me if I am wrong in interpreting the past discussion on this Forum.
Thanks And Regards Smile
Dipak D Gaikwad
Back to top
View user's profile Send private message
mkalgal
Silver Sponsor
Silver Sponsor


Joined: 26 Jan 2003
Posts: 54

PostPosted: Wed Dec 24, 2008 7:23 pm    Post subject: Reply with quote

Dear All

Detailing in post-tensioned flat slabs is very critical. An interesting article can be found on detailing for bonded PT strands at
http://www.ptia.org.au/Photos/Practical%20Prestress%20Detailing.pdf
This may not be the practice followed in toto everywhere, but is worth reading

Cheers!

Kalgal
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conferences-2008 [ Flat Slab Design issues ] All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy