PostPosted: Thu Sep 29, 2011 7:40 am    Post subject: Floating Column Reply with quote
I am designing a G+13 building in etabs. The building has some of the
columns stubbed at 1st floor and the upper 12 floors are supported by
floating columns which are resting on beam at first floor lvl (please
see attached file). Two of the floating columns FC1 & FC2 having
different orientations are resting on the same beam.My problem is how
do I rest these floating columns (FC1 & FC2) on a single beam in etabs
Mustafa Ahmed
Floating_col-Model.pdf
 Filename:  Floating_col-Model.pdf
 Filesize:  737.02 KB
 Downloaded:  1051 Time(s)
Thankful People
ajayapc
PostPosted: Fri Sep 30, 2011 4:11 am    Post subject: Floating Column Reply with quote
Dear SaahilPl don't even attempt to model or recommend floating columns in any buildings considering its vulnerability in eq/lateral loads. You may rethink appropriately and plan columns accordingly.
_Sincerely yours ... __________________________________
Ajay Chourasia
On Thu, 29/9/11, saahil <forum@sefindia.org> wrote:
Subject: [SEFI] Floating Column
Date: Thursday, 29 September, 2011, 2:47 PM
Mustafa Ahmed
Download Attachments:
suresh_sharma
PostPosted: Fri Sep 30, 2011 1:07 pm    Post subject: Reply with quote
AJAY,what you have said about floating columns is theoretically correct but architects have been doing the audacity of providing floating columns.
sakumar79
PostPosted: Sat Oct 01, 2011 1:49 am    Post subject: Reply with quote
   While I agree that architects use floating columns indiscriminately, one should take into account that the building is G+13 and not just G+1 or G+2. Under the circumstances, I feel floating columns should be strictly avoided. Even when you design only vertical load, if you try to design the first floor beam for the floating column load taking into account the high shear and moments, I think the beam depth would be greater than the stilt floor height.
   Hence I strongly suggest you get the architect to avoid the floating columns
Yours sincerely,
Arun
PostPosted: Sat Oct 01, 2011 4:17 am    Post subject: Floating Column Reply with quote
Floating columns must be avoided as much as possible.
Transfer beam must be wide enough to accommodate both
the columns with different orientation of long dim
Transfer beam has be adequate and ,in case adjoining space is not
double height, the provision of orthogonal beams at floating column
locations connected to transfer girder will be structurally better.
May please refer earlier detailed postings by eminent
members since this topic is discussed many times.
best regds
vikramjeet
sakumar79
PostPosted: Sat Oct 01, 2011 11:02 am    Post subject: Reply with quote
   In continuation of Er. Vikramjeet's post, I would like to add one point. If your transfer girder is made wide to accomodate two floating columns, and if the columns are not aligned to the transfer girder, the point torsion in the transfer girder due to the eccentricity should be considered. This should be avoided since the torsion will be very large...
    Again, I reiterate that for a G+13 building, dont go for floating columns.
Arun
rg.gupta
PostPosted: Sat Oct 01, 2011 2:33 pm    Post subject: Floating Column Reply with quote
dear sefians
jai hind
i also aggree with the views of all sefians who have expressed not to
go for such a option as it is very dangerous from the point of
stability and design as in this case
the vertical seismic will be alarmingly high, whereas in other normal
cases this is very negligible but here it is very defirent because of
modal masses are not considing with the supports and hanging on beams
from first floor above.
r g gupta
lele_raj
PostPosted: Sun Oct 02, 2011 12:29 am    Post subject: Floating Column Reply with quote
One of the points which was made known to me for not going for floating column: Go for floating column only if you can provide a perfectly hinged joint, i.e. no transfer of moments, like a "ball" type joint. Any slight eccentricity will put huge BM (or torsion, depending on the direction) on the girder, yielding the floating column quite un-economical.
Best regards,
Rajendra (Raj) Lele
Sent: Sunday, 2 October 2011 5:38 AM
Subject: [SEFI] Re: Floating Column
           dear sefians
jai hind
r g gupta
suresh_sharma
PostPosted: Sun Oct 02, 2011 8:09 am    Post subject: Reply with quote
Dear Sri Gupta,
Why the vertical seismic will be vey high in case of floating columns?
Please elaborate.
prof.arc
PostPosted: Sun Oct 02, 2011 11:13 pm    Post subject: Floating Column Reply with quote
the confusion is because of misnomer - floating COLUMN
It is not a column at all - it is just a vertical member but not transferring load directly to the foundation
May be "Secondary Column" [like nomenclature of Secondary Beam] might be more appropriate.
A true Column on the other hand must start from the Foundation level.
Theoretically, nothing wrong with with such secondary column
But in practice, the joints are poorly analysed, designed and constructed
The most important part of a building are the columns in the lowest floor between foundation and first floor
and those columns are overstressed for horizontal loads - behaving like a stilt.
ARC
On Sun, Oct 2, 2011 at 12:03 PM, lele_raj <forum@sefindia.org (forum@sefindia.org)> wrote:
Page 1 of 5