Hello,
I'm new to practicing engineering. I've come across minute things in practice , which we generally overlook during studies, that become great hindrance during construction.
Problem is: I'm unsure about the verticality of columns and their alignment. It's easier to assume a vertical column for design purpose but here I see it's rather hard to ensure so.
I request the experienced personnel put light on how the alignment & verticality of column is ensured during construction.
Thank you!
PS:
Condition is: Foundation has to be laid & column reinforcement be placed on it and ensured it's vertical & aligned prior to applying form-work & concreting. |
|
Back to top |
|
 |
Dr. N. Subramanian General Sponsor


Joined: 21 Feb 2008 Posts: 5335 Location: Gaithersburg, MD, U.S.A.
|
Posted: Wed May 02, 2012 2:42 pm Post subject: Re: how to ensure columns are vertical & aligned?? |
|
|
Dear Mr Pujan,
Simple Plum bob will show whether the column is vertical or not! The instrument has been used since the time of ancient Egypt to ensure that constructions are "plumb", or vertical.
Best wishes
NS
PujanG wrote: | Hello,
I'm new to practicing engineering. I've come across minute things in practice , which we generally overlook during studies, that become great hindrance during construction.
Problem is: I'm unsure about the verticality of columns and their alignment. It's easier to assume a vertical column for design purpose but here I see it's rather hard to ensure so.
I request the experienced personnel put light on how the alignment & verticality of column is ensured during construction.
Thank you!
PS:
Condition is: Foundation has to be laid & column reinforcement be placed on it and ensured it's vertical & aligned prior to applying form-work & concreting. |
_________________ <p>
Dr.Subramanian Narayanan
</p>
23 Napa Valley Road, Gaithersburg, MD 20878 USA
<p>
</p>
(cdcstruct.com) |
|
Back to top |
|
 |
PujanG SEFI Member

Joined: 30 Mar 2012 Posts: 11
|
Posted: Wed May 02, 2012 3:04 pm Post subject: |
|
|
Thank you sir! |
|
Back to top |
|
 |
a-n-k-u-r Progressive Member


Joined: 19 Mar 2012 Posts: 40 Location: Ghaziabad
|
Posted: Sat May 05, 2012 11:13 am Post subject: |
|
|
As SIr has Said ,
the veritcality of columns needs to be checked using plumb bob . or if in case one is not having at that instant of checking one can use a tape , stone connected with thread. two rods coming out from on each face of the column shuttering.
During checking , drop the stone from the rods attached and check the distance from the shuttering, on the top, bottom and middle .
they should come equal or with an error of 4-5 mm as stated in the SOW . _________________ With Regards,
Ankur Dubey |
|
Back to top |
|
 |
es_jayakumar General Sponsor

Joined: 24 Nov 2011 Posts: 1250 Location: Cochin
|
Posted: Sun May 06, 2012 12:02 pm Post subject: |
|
|
Hi,
The verticality of a column needs to be checked using a plumb bob over the formwork box just before casting. It should be done preferably at the four faces of the box ( or at least two adjacent sides). It should again be checked after casting the column to check and rectify the loss in plumb due to the possible tilt of the box during compaction by vibrator etc.
Regards,
ES Jayakumar |
|
Back to top |
|
 |
spsvasan ...

Joined: 18 Dec 2008 Posts: 327
|
Posted: Mon May 07, 2012 6:58 am Post subject: |
|
|
Dear Mr.Pujan
The verticality of the column shall be checked as indicated by the various engineers. In addition, you have to ensure proper alignment of the columns.
For this, after the plinth beams are cast and after each floor slab is cast, starters or kickers are cast. This is a 75mm height of column. Good quality rigid shuttering is provided for starters. The correct locations of the columns are marked on the slab or over the plinth beam. The kicker shutters are then fixed at the correct theoretical locations and concreted. Usually all starters along one line are cast together.
Once the starters are in correct position, checking of plumb is sufficient to ensure that the columns are in correct position and to plumb.
At each floor level the starters have to be cast.
With best wishes
S.P.Srinivasan |
|