Minimum Reinforcement in Pile ?
patilamol86
PostPosted: Wed Aug 08, 2012 4:07 am    Post subject: Minimum Reinforcement in Pile ? Reply with quote
Dear Friends,
Kindly confirm the minimum reinforcement in pile whether its 0.4% as per IS code or 1.25%  as per books
I have attached the snaps from book BC PUNMIA/RAMAMURTAM they all said same philosophy that 1.25% upto 30D and then increases as per length of pile.
I didnt found these clauses in code which are written in the books but all authors are saying same philosophy it means they are following the same referance.
What is your opinion  ?
Foundation Design.pdf
 Filename:  Foundation Design.pdf
 Filesize:  155.99 KB
 Downloaded:  1824 Time(s)
er.mvv
PostPosted: Thu Aug 09, 2012 5:40 am    Post subject: Re Reply with quote
Dear Patil
      Minimum % shall be 0.4% as per IS:2911 (Part-1/Sec-2)-1979. Since we follow the codes, you can proceed with the above clause.
best regards
    MVV
Dear SENIOR SAFIANs
         Please comment on the above issue raised by Patil.
best regards
     MVV
patilamol86
PostPosted: Fri Aug 10, 2012 3:25 am    Post subject: Reply with quote
Dear SENIOR SAFIANS
Please comment on this Issue
structwell
PostPosted: Fri Aug 10, 2012 5:35 pm    Post subject: minimum reinforcement in pile Reply with quote
Dear Patil
The percentage of steel for Cast in-situ piles min 0.4% of C/s area of pile. Since the reinforcement is not accounted in load calculation of cast in-situ piles. only the unreinforced concrete strength is taken in structural capacity of the pile. For Precast piles the percentage of steel is based on L/D ratio (i.e 1.25%) for withstand the handling stress, driving stress.
Kamaraj.B
Structural Engineer.
patilamol86
PostPosted: Mon Aug 13, 2012 4:15 am    Post subject: Reply with quote
Dear Kamaraj
Thank you for your response but in the books they didnt mention the Precast piles they
just wrote RC pile reinforcement.
I appreciate you, if you gave the reference document for this
Amol Patil
mukeshkumar121in@gmail.co
PostPosted: Sat Jun 09, 2018 2:42 pm    Post subject: Minimum reinforcement in pile Reply with quote
Dear Mr Patil
If the pile is bored cast in situ,then the minimum reinforcement required is 0.4 percent of gross cross sectional area as per IS -2911.
If the pile is pre cast,then the reinforcement should be as per IS-2911 part 1 section 3.It depends upon l/D ratio and varies from minimum 1.25 percent to 1.5 percent of cross sectional area.The same is mentioned in BC Punmia Sir book which you have provided as attachment.It is required for lifting and handling stress.