Tall Building Design :: Framing System
Goto page 1, 2  Next
 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conference on Tall Buildings
View previous topic :: View next topic  
Author Message
bijay sarkar
...
...


Joined: 14 Dec 2009
Posts: 314

PostPosted: Wed Nov 21, 2012 4:56 pm    Post subject: Tall Building Design :: Framing System Reply with quote

Dear Sir,

Can some one describe the different types of major structural systems (along with the description of force flow path of each system) already used worldwide in such Tall Buildings ?


With Regards,

Bijay Sarkar
Back to top
View user's profile Send private message
S.KANTHIMATHINATHAN
SEFI Member
SEFI Member


Joined: 09 Jun 2012
Posts: 12

PostPosted: Fri Nov 23, 2012 5:52 am    Post subject: Tall Building Design :: Framing System Reply with quote

Dear Sirs,
Structural system
1) Braced
2) Unbraced
3) Combination of both

In my opinion, tall structures should be braced in vertical and horizontal planes. If floors are R.C.C , the same provides rigid diaphragm action.

Load path

Vertical load- floor beam to column as reaction ( with moment in case of fixed beam )
Horizontal loads ( due to wind & seismic) - through bracing members.

With kind regards,
S.Kanthimathinathan
Structural Engineering Consultant,
Tiruchy Engineering Consultancy House,
1/1-A.Nariyan Street,
Srirangam, Tiruchy-620006
( Courses offered:- Design & Detailing of steel & R.C.C Structures)



Subject: [E-CONF] Tall Building Design :: Framing System
From: forum@sefindia.org
Date: Wed, 21 Nov 2012 22:26:24 +0530
To: econf34289@sefindia.org

           Dear Sir,

Can some one describe the different types of major structural systems (along with the description of force flow path of each system) already used worldwide in such Tall Buildings ?


With Regards,

Bijay Sarkar

Posted via Email
Back to top
View user's profile Send private message
gautam chattopadhyay
...
...


Joined: 17 Feb 2009
Posts: 128

PostPosted: Sun Nov 25, 2012 7:58 am    Post subject: Tall Building Design :: Framing System Reply with quote

Is it very necessay for buildings up to 50 m to brace the external columns? If we place the shear walls judicially with sufficient srtuctural sense I think the horizontal forces will be resisted jointly by the shear walls and the columns. It must be admitted that center of stiffness and center of mass do never coincide, and columns/shear walls cannot be placed in that way. If done it will be a ridiculous design. Practicality must be addressed to. In some older buildings in Delhi and Calcutta I have seen braced columns at external peripherry. They are standing well but the buildings where such measures have not been taken are also performing well.

On Fri, Nov 23, 2012 at 11:50 AM, S.KANTHIMATHINATHAN <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           Dear Sirs,
Structural system
1) Braced
2) Unbraced
3) Combination of both

In my opinion, tall structures should be braced in vertical and horizontal planes. If floors are R.C.C , the same provides rigid diaphragm action.

Load path

Vertical load- floor beam to column as reaction ( with moment in case of fixed beam )
Horizontal loads ( due to wind & seismic) - through bracing members.

With kind regards,
S.Kanthimathinathan
Structural Engineering Consultant,
Tiruchy Engineering Consultancy House,
1/1-A.Nariyan Street,
Srirangam, Tiruchy-620006
( Courses offered:- Design & Detailing of steel & R.C.C Structures)



Subject: [E-CONF] Tall Building Design :: Framing System
From: forum@sefindia.org (forum@sefindia.org)
Date: Wed, 21 Nov 2012 22:26:24 +0530
To: econf34289@sefindia.org (econf34289@sefindia.org)

           Dear Sir,

Can some one describe the different types of major structural systems (along with the description of force flow path of each system) already used worldwide in such Tall Buildings ?


With Regards,

Bijay Sarkar
     



     



Posted via Email
Back to top
View user's profile Send private message
biju
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 6
Location: Mumbai

PostPosted: Mon Nov 26, 2012 9:40 am    Post subject: Re: Tall Building Design :: Framing System Reply with quote

Framing system plays a very vital role in the design of Tall buildings.
At the very beginning of a project, at the concept stage, if the Architect and Structural Eng. sit together and finalize the column/Shear wall locations, then much effectiveness in the design can be arrived at.

If it is a concrete structure, then as Mr. Chattopadhyay has mentioned, CM and CR has to coincide as far as possible. Proper load path has to be defined. Stiffness along the height has to be such that wind induced accelerations and deflections are well under control.

Stress levels in the compression members are to be proportioned, so that axial shortening effect is under check. And of course, optimum foundation system has to be arrived at, with proper stability check.

regards,

Biju






[quote="gautam chattopadhyay"]Is it very necessay for buildings up to 50 m to brace the external columns? If we place the shear walls judicially with sufficient srtuctural sense I think the horizontal forces will be resisted jointly by the shear walls and the columns. It must be admitted that center of stiffness and center of mass do never coincide, and columns/shear walls cannot be placed in that way. If done it will be a ridiculous design. Practicality must be addressed to. In some older buildings in Delhi and Calcutta I have seen braced columns at external peripherry. They are standing well but the buildings where such measures have not been taken are also performing well.
Back to top
View user's profile Send private message
kapildingare
...
...


Joined: 15 May 2009
Posts: 103

PostPosted: Mon Nov 26, 2012 12:56 pm    Post subject: Reply with quote

Resp. Chattopadhayji,
Your views
“If we place the shear walls judicially with sufficient srtuctural sense I think the horizontal forces will be resisted jointly by the shear walls and the columns. It must be admitted that center of stiffness and center of mass do never coincide, and columns/shear walls cannot be placed in that way. If done it will be a ridiculous design. Practicality must be addressed to.”
What I think that framing system , with shear walls , in which centre of stiffness and centre of mass does not coincide, presence of shear walls itself is creating more problems than giving solutions.
I would like your expert opinion in selecting frame system,
1)     Framing system in which shear walls placed with eccentricities with respect to center of mass.
2)     Framing system in which columns are diagonally braced and such frame is resisting lateral loads.

Would like your attention on photos of
1)     Bhuj Earthquake : RCC Building failure with lift/stair case with rcc walls standing erect.
2)     Cover photo on mag. Earthquake Engineering Practices—Sept 2012 (NICEE)


Thank you,

                                                               Kapil Dingare
Back to top
View user's profile Send private message
gautam chattopadhyay
...
...


Joined: 17 Feb 2009
Posts: 128

PostPosted: Thu Nov 29, 2012 6:10 am    Post subject: Tall Building Design :: Framing System Reply with quote

You are true, in fact very true to say eccentric shear walls pose bigger problem in distribution of storey forces. I told you we cannot place our shear walls at our wills since then the internal arrangement of columns will become very ridiculous from architectural point of view. We have to compromise somewhere. Your proposal of braced column is nothing but an open web shear wall but again, architecturally will it look good? we have to think pragmatically and have to serve all the purposes - service, beauty, comfort of end users - all. What I feel, in normal course of working never the center of stiffness and center of mass will coincide. Ok, how much will be the storey torsion? by how much will your storey shear increase? How much will be additional shear and moment on the columns and shear walls? can we not provide some additional reinforcements for the same?

On Mon, Nov 26, 2012 at 6:26 PM, kapildingare <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           Resp. Chattopadhayji,
Your views
“If we place the shear walls judicially with sufficient srtuctural sense I think the horizontal forces will be resisted jointly by the shear walls and the columns. It must be admitted that center of stiffness and center of mass do never coincide, and columns/shear walls cannot be placed in that way. If done it will be a ridiculous design. Practicality must be addressed to.”
What I think that framing system , with shear walls , in which centre of stiffness and centre of mass does not coincide, presence of shear walls itself is creating more problems than giving solutions.
I would like your expert opinion in selecting frame system,
1)     Framing system in which shear walls placed with eccentricities with respect to center of mass.
2)     Framing system in which columns are diagonally braced and such frame is resisting lateral loads.

Would like your attention on photos of
1)     Bhuj Earthquake : RCC Building failure with lift/stair case with rcc walls standing erect.
2)     Cover photo on mag. Earthquake Engineering Practices—Sept 2012 (NICEE)


Thank you,

                                                             Kapil Dingare
     



     


Posted via Email
Back to top
View user's profile Send private message
baldevprajapati
SEFI Member
SEFI Member


Joined: 27 Aug 2012
Posts: 13

PostPosted: Sun Dec 02, 2012 10:39 am    Post subject: Reply with quote

hallo sir r  u know the  design of tall building by Etabs ?
Back to top
View user's profile Send private message
baldevprajapati
SEFI Member
SEFI Member


Joined: 27 Aug 2012
Posts: 13

PostPosted: Sun Dec 02, 2012 10:45 am    Post subject: Reply with quote

i have a problem to design 30 story building By etabs & ISMB600 section  is limit in the code , these section is fail so i how to sole the these probleme
thank u sir
Back to top
View user's profile Send private message
thirumalaichettiar
Silver Sponsor
Silver Sponsor


Joined: 26 Jan 2003
Posts: 3459

PostPosted: Sun Dec 02, 2012 11:34 am    Post subject: Reply with quote

baldevprajapati wrote:
hallo sir r  u know the  design of tall building by Etabs ?


Hallo" Mr.Baldevprajapati,

You are welcome to post in one place and it will be noticed by all sefians. You have posted in 3 places the same question in 3 different topic.

Kindly avoid doing so to save time of seniors and spce of Sefi forum.

T.Rangarajan.
Back to top
View user's profile Send private message
thirumalaichettiar
Silver Sponsor
Silver Sponsor


Joined: 26 Jan 2003
Posts: 3459

PostPosted: Sun Dec 02, 2012 11:37 am    Post subject: Reply with quote

baldevprajapati wrote:
i have a problem to design 30 story building By etabs & ISMB600 section  is limit in the code , these section is fail so i how to sole the these probleme
thank u sir


Er.Baldevprajapati,

If the section is the maximum one and if you need to use a section of your choice in ETAB you have the option of SECTION DESIGN under the frame section in which you can create your own section. Refer the manual for more details.

General:
Can you check your spelling and grammer before posting using the spell check provisions in the program? It will help yourself and also others to understand what you are posting.

T.RangaRajan.
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conference on Tall Buildings All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy