Last floor column design
Goto page 1, 2, 3, 4, 5  Next
 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conference on Tall Buildings
View previous topic :: View next topic  
Author Message
vijaydshah
SEFI Regulars
SEFI Regulars


Joined: 15 Nov 2011
Posts: 20

PostPosted: Wed Nov 28, 2012 12:48 pm    Post subject: Last floor column design Reply with quote

Dear sefians
It has been observed from the experience that for all buildings when we do space frame analysis the reinforcement of the last floor is quite high compared to lower stories . This is specifically for the end columns where moment distribution is not possible due to discontinuity of the columns. Providing this reinforcement through out the height of the building do not justify the economy.

Can any one throw light on this subject ?.

_________________
vdshah
Back to top
View user's profile Send private message
Thankful People
1 user(s) is/are thankful for this post.
Manoharbs_eq
General Sponsor
General Sponsor


Joined: 17 Jul 2012
Posts: 423

PostPosted: Wed Nov 28, 2012 2:09 pm    Post subject: Last floor column design Reply with quote

Of coarse its true, but at lower levels load is governing so steel is higher , its uneconomical to provide last floor higher reinf throughout it should be reduced gradually so to achieve economy reduce it every two floors
On 28-Nov-2012 7:30 PM, "vijaydshah" <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           Dear sefians
It has been observed from the experience that for all buildings when we do space frame analysis the reinforcement of the last floor is quite high compared to lower stories . This is specifically for the end columns where moment distribution is not possible due to discontinuity of the columns. Providing this reinforcement through out the height of the building do not justify the economy.

Can any one throw light on this subject ?.
     


vdshah
     



     


Posted via Email
Back to top
View user's profile Send private message
irfan_ahmed
SEFI Member
SEFI Member


Joined: 19 Jul 2010
Posts: 4

PostPosted: Wed Nov 28, 2012 2:10 pm    Post subject: Last floor column design Reply with quote

There are two ways - either provide higher reinforcement for top most story column or while analyzing assign top joint as hinged. However by doing so there are chances that the inter story drift for the top most story exceeds the limit. - from Vodafone
From: "vijaydshah" <forum@sefindia.org>
Date: Wed, 28 Nov 2012 18:18:27 +0530
To: <econf34289@sefindia.org>
ReplyTo: econf34289@sefindia.org
Subject: [E-CONF] Last floor column design

     Dear sefians  It has been observed from the experience that for all buildings when we do space frame analysis the reinforcement of the last floor is quite high compared to lower stories . This is specifically for the end columns where moment distribution is not possible due to discontinuity of the columns. Providing this reinforcement through out the height of the building do not justify the economy.   Can any one throw light on this subject ?.
     vdshah
        --

Posted via Email
Back to top
View user's profile Send private message
SameerDhuri
SEFI Member
SEFI Member


Joined: 01 May 2012
Posts: 5

PostPosted: Wed Nov 28, 2012 2:44 pm    Post subject: Re: Last Floor Column Reply with quote

Er Vijay Sir,
                       The above problem of heavy steel in Last Floor Column can be tackled by Reverse lapping Heavy diameter Steel Bars in last floor Column with lower dia bars for eg. 20 mm dia bars can be lapped with 16 mm dia bars.
I request Senior Sefians to comment on the appropriate way of dealing this problem especially in cases where there are Swimmimg pools on the roof! which increases the Lateral Force in last floor column.

Best Regards,
SameerDhuri
samsdhuri@gmail.com
Back to top
View user's profile Send private message
Surendra S
SEFI Member
SEFI Member


Joined: 25 Sep 2009
Posts: 16

PostPosted: Thu Nov 29, 2012 2:11 am    Post subject: Last floor column design Reply with quote

Your r right Vijay,

You can go with higher reinforcement at top most floor


rgds
SS

On Wed, Nov 28, 2012 at 9:52 PM, irfan_ahmed <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           There are two ways - either provide higher reinforcement for top most story column or while analyzing assign top joint as hinged. However by doing so there are chances that the inter story drift for the top most story exceeds the limit. - from Vodafone
From:  "vijaydshah"
Date: Wed, 28 Nov 2012 18:18:27 +0530
To:
ReplyTo:  econf34289@sefindia.org (econf34289@sefindia.org)
Subject: [E-CONF] Last floor column design

     Dear sefians It has been observed from the experience that for all buildings when we do space frame analysis the reinforcement of the last floor is quite high compared to lower stories . This is specifically for the end columns where moment distribution is not possible due to discontinuity of the columns. Providing this reinforcement through out the height of the building do not justify the economy. Can any one throw light on this subject ?.

     vdshah
      --
     



     



Posted via Email
Back to top
View user's profile Send private message
sriprakash_shastry
...
...


Joined: 23 Mar 2010
Posts: 50

PostPosted: Thu Nov 29, 2012 4:09 am    Post subject: Reply with quote

Dear Mr. Shah.

There is another angle to your question. What you are saying is absolutely right. But, I also find that if there is a building of 20 floors, I find some engineers detailing only one floor and then repeating the same thing in all the floors.

I dont think this is a right approach. For tall buildings the stiffness of the columns reduce as you keep going to the top. In effect the columns in the lower floors are stiffer than the columns in the upper floor. Stiffer columns tend to attract more force than non-stiff columns. As the force in stiffer columns is more the distribution of forces within the floor are also different.

In a very tall building it may be advisable to have similar reinforcement for every 5 floors, but I dont think it would be economical to have the same reinforcement in beams for all the floors.

Regards,

Sriprakash
Back to top
View user's profile Send private message
gautam chattopadhyay
...
...


Joined: 17 Feb 2009
Posts: 129

PostPosted: Thu Nov 29, 2012 5:11 am    Post subject: Last floor column design Reply with quote

This happens because at top most storey direct load is much less and moment is very high.

On Thu, Nov 29, 2012 at 9:39 AM, sriprakash_shastry <forum@sefindia.org (forum@sefindia.org)> wrote:
Quote:
           Dear Mr. Shah.

There is another angle to your question. What you are saying is absolutely right. But, I also find that if there is a building of 20 floors, I find some engineers detailing only one floor and then repeating the same thing in all the floors.

I dont think this is a right approach. For tall buildings the stiffness of the columns reduce as you keep going to the top. In effect the columns in the lower floors are stiffer than the columns in the upper floor. Stiffer columns tend to attract more force than non-stiff columns. As the force in stiffer columns is more the distribution of forces within the floor are also different.

In a very tall building it may be advisable to have similar reinforcement for every 5 floors, but I dont think it would be economical to have the same reinforcement in beams for all the floors.

Regards,

Sriprakash
     



     


Posted via Email
Back to top
View user's profile Send private message
Dr. N. Subramanian
General Sponsor
General Sponsor


Joined: 21 Feb 2008
Posts: 5538
Location: Gaithersburg, MD, U.S.A.

PostPosted: Thu Nov 29, 2012 5:30 am    Post subject: Reply with quote

Dear Er Sriprakash,

I do not follow what you are trying to say! I feel that the beam reinforcement will be almost same in all floors and only the column reinforcement will change.

It is a better practice to have same size of column throughout the height or at least for a few floors and change only the rebars. As Er Shah says, there will be more moments at the top floor and more axial force in the bottom floor. We can have 10 to 15 percent more reinforcement in top floor,
If it exceeds that limit, better to provide that rebars in the bottom columns also. That is the reason for the suggestion of keeping the same size of column. If the column size is reduced, the leaver arm to resist bending will be reduced and hence we may need still more rebars at the top level.

The stiffness of column also depends on the extent of cracking!In IS code there is no provision for that- ACI code gives some formula, I think it also depends on axial load.

Best wishes,
NS
sriprakash_shastry wrote:
Dear Mr. Shah.

There is another angle to your question. What you are saying is absolutely right. But, I also find that if there is a building of 20 floors, I find some engineers detailing only one floor and then repeating the same thing in all the floors.

I dont think this is a right approach. For tall buildings the stiffness of the columns reduce as you keep going to the top. In effect the columns in the lower floors are stiffer than the columns in the upper floor. Stiffer columns tend to attract more force than non-stiff columns. As the force in stiffer columns is more the distribution of forces within the floor are also different.

In a very tall building it may be advisable to have similar reinforcement for every 5 floors, but I dont think it would be economical to have the same reinforcement in beams for all the floors.

Regards,

Sriprakash
Back to top
View user's profile Send private message
sriprakash_shastry
...
...


Joined: 23 Mar 2010
Posts: 50

PostPosted: Thu Nov 29, 2012 5:47 am    Post subject: Reply with quote

Dear Dr. NS

I have found that in some analytical models that the reinforcement in the beams in the floors lets say between the 15th and 20th floors are lesser than the reinforcement in between the 1st and the 5th floors although the loads on the floors are the same.

I was attributing this to the reduction in the stiffness of the columns. Can you tell me why this could possibly be happening.

Warm Regards,

Sriprakash
Back to top
View user's profile Send private message
kapildingare
...
...


Joined: 15 May 2009
Posts: 104

PostPosted: Thu Nov 29, 2012 6:38 am    Post subject: Reply with quote

Resp Dr Subramanian,

                               Even for six storey building beam forces and hence reinforcement changes with respect to storey height,when we analysis frame for lateral loads.
                                         Please guide me further and I request you to be in eC up to last moment so we can have your guidance.

                                         Thank you,very much.



                                                              Kapil Dingare
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conference on Tall Buildings All times are GMT
Goto page 1, 2, 3, 4, 5  Next
Page 1 of 5

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy