inchak at tatasteel.com Guest
Posted: Mon Jul 04, 2005 7:14 am Post subject: How does embossing affect Bond Strength? |
Dear Mr. H.S.Rai
You have indeed raised a very valid point.
We did carry out elaborate pull out test for all sections with the embossed part embedded in concrete. The results are tabulated below. FOR 0.025 MM Slip (Specified Ratio 140%)
Size Load Plain Load TMT Actual Ratio of Load for (mm) (Kg) (Kg) TMT / Plain bar (%)
8.00 125 450 360 10.00 120 210 175 12.00 290 470 162 16.00 610 940 154 20.00 650 1160 178 36.00 1280 3100 242
FOR 0.25 MM Slip (Specified Ratio 180%)
8.00 310 1305 421 10.00 615 1400 228 12.00 1190 2270 191 16.00 1650 4030 244 20.00 3600 8630 240 36.00 6500 16250 250
It clearly shows that the actual bond strength is way above what is required by the specification.
We have also carried out calculation of Ar values completely ignoring the projected area provided by the embossed characters and taking into account the transverse ribs on only one side. The calculated Ar values are also well above what is required by the specification.
Trust this puts your doubts at rest.
********************************DISCLAIMER*********************************** Information contained and transmitted by this e-mail is confidential and proprietary to Tata Steel Ltd. and is intended for use only by the addressee. If you are not the intended recipient , you are notified that any dissemination or copying of this e-mail is strictly prohibited and you are requested to delete this e-mail immediately and notify the originator. Tata Steel does not enter into any binding agreement with any party by e-mail. Any views expressed by an individual do not necessarily reflect the view of Tata Steel. Tata Steel is not responsible for the consequences of any actions taken on the basis of information provided. While this e-mail has been checked for all known viruses the addressee should also scan for viruses. To know more about Tata Steel please visit www.tatasteel.com ********************************************************************************