How to calculate Temperature load for steel structures.
StrARS
PostPosted: Tue Nov 04, 2014 7:01 am    Post subject: How to calculate Temperature load for steel structures. Reply with quote
The below values related to temperature load from my project specification, i cant understand this. anyone please explain me about this and what value to be given in staad pro... please help me as soon as possible.
DESIGN TEMPERATURE VARIATION
The temperature load will be assessed based on the recommendations of BS EN 1991-1-5:2003 Actions on structures Part 1-5: General actions Thermal actions. The design temperature range will be defined as the difference between the highest and the lowest one day mean temperature, plus the temperature of the steel due to solar gain. The following parameters have been used:
Tmin = 14C
Tmax = 41C
Tsolar = 20C
Tin = 20C
Tout = Tmax + Tsolar = 61C
ΔT = Tout Tmin = 47C
The difference between the highest and lowest one day mean temperatures is 27C.
The temperature range due to solar gain is 20C.
Therefore, the total temperature range under consideration for structural steelwork = 47C
Note that the temperature variation is only significant during construction, and temporary stresses may be relieved by sliding joints. Once insulation has been installed, the structural temperature variation will be significantly reduced.
Arun S
amol_acharya
PostPosted: Tue Nov 04, 2014 10:56 am    Post subject: Reply with quote
Dear SEFIan,
Please see attached the proposed methods of calcualting the temp. defferential.
I hope this will solve your problem. Unfortunately not much of data is available in this matter. I suggest that all fellow SEFIan should contribute this this matter to come up with a correct solution...
How to Calculate DT ?
Method-1:
Max. Summer Temp. = 40 C
Least Winter Temp. = 12 C
Temp. Deferential DT = (40 12)/2 = 28 =  14 C          (+/-)
Method-2:
Mean Temp. = 27 C at the Time of concreting
Temp. Deferential DT+  = 40 27 = 13 C          (+)
Temp. Deferential DT-   = 27 12 = 15 C           (-)
Method-3: As per the attachment is as per the National Academy of sciences USA, which needs to be studied further.
Amol Acharya
Temperature Analysis.pdf
 Filename:  Temperature Analysis.pdf
 Filesize:  407.14 KB
 Downloaded:  721 Time(s)
nitin_chandavar
PostPosted: Tue Sep 11, 2018 10:30 am    Post subject: Temperature load calculation Reply with quote
could you please give the reference for Method-3 ( National Academy of science publication reference.)
amol_acharya wrote:
Dear SEFIan,
Method-1:
Method-2:
Amol Acharya
karthick_ce
PostPosted: Wed Sep 12, 2018 5:30 pm    Post subject: How to calculate Temperature load for steel structures. Reply with quote
Please refer EN 1991-1-4 for detail procedure to calculate the temperature difference load.
Sent from my Windows Phone