Sudhakaran General Sponsor
Posted: Fri May 27, 2016 3:29 pm Post subject: Raft analysis and Design |
Dear sefians,
A tool for analysis and design of raft for irrigation structure attached herewith.
Click on reset(to clear stored values)
Then enter the loads from right edge of raft and distance from right edge of raft to the each load.
Click on analysis and then design and report
It is for uniform width of 1m.
Sudhakaran
 Download |
Filename: |
Raft.rar |
215.5 KB |
Downloaded: |
1130 Time(s) |
VPandya General Sponsor
Posted: Sat May 28, 2016 4:16 am Post subject: Also use ACI 152.1 for RAFT ANALYSIS & DESIGN. |
Dear Er. Sudhakaranji,
There is a very widely used ACI Publication on RAFT ANALYSIS AND DESIGN. I use this:
ACI SP 152-1
An Introduction to the
State-of-the-Art Mat/Raft Foundation
Design and Construction
by E. J. Ulrich, Jr.
Synopsis: Subgrade response is the most important parameter in
analyzing and designing mat foundations. Rational design of a mat
foundation requires the consideration of immediate and long term
subgrade response. "
This publication recommends using PLATE & SHELL ELEMENTS ( PLATE FINITE ELEMENT METHOD) of let us say STAAD/PRO for RAFT CONCRETE and Soil Springs ( Wiinkler Springs) for modeling soil. There are some 3 actual case studies ( High Rise Buildings) of RAFT ANALYSIS & DESGN supporting 50 stories Structure.
Note: Recently I was involved in Checking a RAFT ANALYSIS & DESIGN of a Major Structure ( Heavy Loads), and Design Engineers did RAFT Analysis and Design without using this document ACI SP-152-1, and results were disappointing. What does it take to use this ACI SP-152-1 and do it right?
Copy of Publication Attached.
Vasudeo Pandya P.E.
Structural Engineer
An Introduction to the State-of-the-Art Mat Foundation Design and Constructi |
 Download |
Filename: |
SP-152.pdf |
3.61 MB |
Downloaded: |
3591 Time(s) |
Posted: Sat May 28, 2016 3:15 pm Post subject: Re: Also use ACI 152.1 for RAFT ANALYSIS & DESIGN. |
Dear Vpandya sir,
Thank you for very useful document.
Thanks,
Sudhakaran
VPandya wrote: | Dear Er. Sudhakaranji,
ACI SP 152-1
This publication recommends using PLATE & SHELL ELEMENTS ( PLATE FINITE ELEMENT METHOD) of let us say STAAD/PRO for RAFT CONCRETE and Soil Springs ( Wiinkler Springs) for modeling soil. There are some 3 actual case studies ( High Rise BUildings) of RAFT ANALYSIS & DESGN supporting 50 stories Structure.
Vasudeo Pandya P.E.
Structural Engineer |
ferozpatthan General Sponsor
Posted: Sun May 29, 2016 5:05 am Post subject: Raft Design documents SP-152 |
Thank you very much for sharing
Posted: Tue Dec 27, 2016 5:26 pm Post subject: RAFT ANALYSIS & DESIGN BY FEM OF STAAD/PRO . |
Dear Sefi Engrs,
Recently a Structural Engineer name Mr. Vasantha Kumar contacted by E-Mail on some query he had on FEM analysis and finding out CORRECT RAFT THICKNESS from such FEM analysis. I gave this attached reply. Please comment on my reply. Comments are more than welcome. In real world changing large Raft Thickness is always a project cost item. They do not like it. But IS 456-2000 Section 40.2.3 and 40.2.3.1 Table-20 limit Tcmax even with Shear Reinf. to 2.0 mpa. I got in one of my FEM analysis max of SQX and SQY ( Plate Element Shear Stress ) = 2.55 mpa. I recommended CHANGE THE RAFT THICKNESS from present design thickness of 3.0 m . At that point they were looking for a GUN TO SHOOT ME.
Please comment.
Dear Er. Vasantha Kumar ,
Sorry I was busy with Christmas Holidays and some socialfunctions ( Marriages ) so could not reply to your query early. ForDirection of Plate & Shell elements forces in STAAD/PRO see Section 1.6.1 PLATE & SHELL ELEMENTS of STAADTECH. REFERENCE MANUAL ( Available online in Help and type Plate and Shell Elements in searchbox) . That tell you what is positive and Negative force in yourout put. See table 1-3 of same section giving TERMS INCLUDED IN THESTRESS ELEMENT OUTPUT . in that table Shear Stresses SQX , SQY ---- ShearStress ( Force/length / thickness) .
So let us say I have done a RAFT FOUNDATION analysis usingPLATE & SHELL ELEMENTS of STAAD/PRO . I willdo this to check THICKNESS of RAFT .
a) Run Analysis.
b) Go to mode in the top Manu bar and selectMODE. Select Post Process.
c) Select or High light all plate elements .
d) Go to report , PLATE STRESSES and select first SQX ( Select from highest to lowest )
e ) This will give you highest SQX any where in theModel or of all elements . Note it down value of stress Max SQX andElement Number.
f) Now do the same report for Max SQY . Notedown value of max SQY and Element number .
Now CHECK ON RAFT THICKNESS ( Assume Raft Thickness is3.0 m ) .
Say output gives you max of SQX or SQY is = 2.52 mpa, Allowable in IS 456-2000 is Shear Stress =2.0 mpa . So 3.0m Raft thickness fails. In this case, You need to increase the RAFT THICKNESS tosay 4.0 m. So do same check for 4.0m Raft Thickness . Whoknows after this Check you may need even a Thicker Raft, say 5.0 m . On a projects I worked which had very HEAVY LOADS , The 3.0m Raft Thickness failed by this check.
Regards.
Vasudeo Pandya P.E.
Structural Engineer
es_jayakumar General Sponsor
Posted: Wed Dec 28, 2016 2:06 am Post subject: |
Dear Pandya Sir,
"Allowable in IS 456-2000 is Shear Stress =2.0 mpa".
Here, do you refer to the punching shear and where is this 2.0 MPa from ?
Posted: Fri Dec 30, 2016 3:08 am Post subject: See IS 456-2000 section 40.2.3.1 & Table-20 |
Dear Er E S Jayakumar ,
We had on that project high strength concrete M 40 and above. So from Table - 20 value for Tcmax ( Maximum Shear Stress in concrete with Shear Reinf. ) is 4.0 mpa.
For Raft ( Solid Slab ) Tc ( Max Allowable Shear Stress in Concrete) is = 4.0/2.0 = 2.0 mpa.
40.2.3.1For solid slabs, the nominal shear stress shall not exceed half the appropriate values given in Table 20.
Regards .
Vasudeo Pandya P.E.
Structural Engineer
sakumar79 ...
Posted: Fri Dec 30, 2016 5:17 am Post subject: |
Dear Er Pandya,
If shear stress is so high in slab (2 N/sqmm), will it not require provision of shear reinforcement? Is shear reinforcement practical in raft slabs and if so can you share us any sample detailing for the same?
In my humble opinion, will it not be better to subdivide the slabs in smaller segments by providing more beams so that the raft slab is suitable for detailing without shear reinforcement rather than making the slab thicker?
Yours sincerely
Arunkumar
Posted: Fri Dec 30, 2016 7:04 am Post subject: |
Thank you, Pandya sir. Is the raft referred by you slab type or slab & beam type ? I hope slab & beam type will help to reduce the thickness of the raft slab.