Vibration - IS 800-2007
Bhushan P D P
PostPosted: Thu Dec 07, 2017 6:24 am    Post subject: Vibration - IS 800-2007 Reply with quote
Using the guidelines given in IS 800, if the beam deflection is less than 13mm, we can manage the frequency around 5 Hz.
But in case of large span beams and trusses, it is difficult to limit to above deflection. In this case how to satisfy codal provisions.
Amol.Taralkar
PostPosted: Thu Dec 07, 2017 8:08 am    Post subject: Reply with quote
Deflection and vibration frequency are two different criteria of serviceability check.
In your post you have mixed them.
Treat deflection and vibration separately.
Deflection Check - as per cl.5.6.1, IS 800:2007
Vibration Check - as per cl.5.6.2 & Annex C, IS 800:2007
Best Regards,
Amol Taralkar
B.V.Harsoda
PostPosted: Fri Dec 15, 2017 4:34 pm    Post subject: Reply with quote
Natural Floor Frequency should be Calculated  with simplified formula given in IS 800:2017 Annex C as below:
     fn (Hz) =18/ ( Dmm)^0.5
       fn (Hz)= Natural Floor Frequency In Hz
       Dmm= Deflection In mm
For large span you  have to increase M. I. to reduce deflection.
Above formula can be used for any support condition.