Column safety consider in IS 13920-2016
prakashsiyani
PostPosted: Fri Aug 10, 2018 7:10 am    Post subject: Column safety consider in IS 13920-2016 Reply with quote
Dear All
I have attached details calculations. Please refer it in details, who interested in 13920-2016 ductility.
Earthquake Combination 6 is govern case for column main steel design.
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
         Shear in minor = 48.89 kN
         Shear in major = 42.54 kN
As per IS13920-2016, Cl.7.2 #8 & Cl.7.5 #10.
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
         Shear in minor = 1029 kN
         Shear in major = 260 kN
         In x direction calculation
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
Increase data due to IS 13920-2016
P= 1631/1631 =0
Mu2 = 590.8/80.84 = 7.34 times
Mu3 = -2321/33.128 = 70.06 times
Shear in minor = 1029/48.59 = 21.17 times
Shear in major = 260/42.54 = 6.11 times
Prakash Siyani
P-Cube Consultants.
IS 13920-2016_Column Design Calculations.pdf
 Filename:  IS 13920-2016_Column Design Calculations.pdf
 Filesize:  1.09 MB
 Downloaded:  316 Time(s)
prakashsiyani
PostPosted: Wed Aug 22, 2018 6:04 am    Post subject: Re: Column design Query_IS 13920-2016 Reply with quote
Dear sir
Please reply us on this topic
share your ideas,
I hope expert structure engineer guide us proper,
prakashsiyani wrote:
Dear All
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
         In X direction calculation
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
         In Y direction calculation
P= 1631/1631 =0
Prakash Siyani
P-Cube Consultants.
saikiran gone
PostPosted: Thu Aug 23, 2018 7:50 am    Post subject: Re: Column design Query_IS 13920-2016 Reply with quote
Dear sir
share your ideas,
Dear All
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
P= 1631/1631 =0
Prakash Siyani
P-Cube Consultants.
Hi Prakash,
As per my knowledge, the analysis is same for ductile & non ductile buildings, the forces variation shown above are very high , literally I shocked with this increase in forces as per 13920-2016. I don't believe this is due to code change, kindly recheck the model.
Saikiran Gone.
prakashsiyani
PostPosted: Sat Aug 25, 2018 8:42 am    Post subject: Re: Column design Query_IS 13920-2016 Reply with quote
Dear Saikiran Gone sir
We agreed with your statement that"analysis is same for ductile and non ductile" but after complete of analysis, Design calculation generate this amount of forces. software design output was checked by manual calculation as attached. if you find any mistake please tell us.
Prakash Siyani
Dear sir
share your ideas,
Dear All
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
P= 1631/1631 =0
Prakash Siyani
P-Cube Consultants.
Hi Prakash,
Saikiran Gone.
prakashsiyani
PostPosted: Thu Aug 30, 2018 5:35 am    Post subject: Re: Column design Query_IS 13920-2016 Reply with quote
Dear sir
share your ideas,
Dear All
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
P= 1631/1631 =0
Prakash Siyani
P-Cube Consultants.
abhio
PostPosted: Thu Aug 30, 2018 12:25 pm    Post subject: Reply with quote
Dear Er Siyani,
You have taken hst = 4.5/2 in your calculation. Is this because the column is terminated at this level?
prakashsiyani
PostPosted: Mon Sep 03, 2018 3:40 am    Post subject: Reply with quote
Yes, sir
Column is terminated at basement slab level
Prakash
abhio wrote:
Dear Er Siyani,
prakashsiyani
PostPosted: Thu Sep 13, 2018 11:28 am    Post subject: Re: Column design Query_IS 13920-2016 Reply with quote
Till date we didn't receive any expert reply with same solution or logic.
please reply of attached photo why this building was not collapse even we tried to collapse row of column.
Prakash
Dear sir
share your ideas,
Dear All
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -33.128 kN-m
Data: P = 1631 kN
         Mu2 = 80.84 kN-m
         Mu3 = -2321 kN-m
      P = 1631 kN
         Mu2 = -590.8 kN-m
         Mu3 = -33.128 kN-m
P= 1631/1631 =0
Prakash Siyani
P-Cube Consultants.
 Filesize:  198.87 KB
 Viewed:  40 Time(s)