Response Spectrum Analysis Scale Factor Input in Etabs v2017
kiranklk
PostPosted: Thu May 23, 2019 11:49 am    Post subject: Response Spectrum Analysis Scale Factor Input in Etabs v2017 Reply with quote
Dear Engineers,
     I just observed some changes in response spectrum analysis scale factor in latest Etabs v17, while defining RS function as per IS:1893-2016. You can see in below images as it is asking to input Importance factor(I) & Response Reduction/Ductility(R) value where as it was not there in previous versions of Etabs. While defining RS load cases as shown in below images we are calculating scale factor value as  SF=Ig/2R, but as per new version we need to input scale factor as acceleration(g). Sa/g values are multiplied by (I/2R) by default.
Default SF = (I/2R)= 1.2/10 = 0.12
Acceleration = Z(PGA) x  Default SF = 0.24 x 0.12 = 0.0288
Defined function table in Etabs
Time Period-----Acceleration(Sa/g)
        0        -----       0.0288
 Filesize:  240.35 KB
 Viewed:  83 Time(s)
 Filesize:  199.56 KB
 Viewed:  94 Time(s)
Poorna
PostPosted: Fri May 31, 2019 6:14 pm    Post subject: Re: Response Spectrum Analysis Scale Factor Input in Etabs v2017 Reply with quote
Yes, only g is the scale factor.
haridevender
PostPosted: Tue Jun 04, 2019 6:29 am    Post subject: Reply with quote
Hi
After enhancement of base shear, whether SPECX or EQX to be considered for further analysis and design? Code mentioned nothing regarding this.
Thanks and Regards
Hari Devender
Poorna
PostPosted: Tue Jun 04, 2019 1:04 pm    Post subject: Reply with quote
I typically use spectrum cases for the design of elements not static EQ cases as the spectrum considers much better distribution of lateral forces.
But for foundation using spectrum is not recommended as it gives absolute (+ve) values, so for foundations i typically use static EQ.
rojanmathewtsy
PostPosted: Thu Jun 06, 2019 7:08 am    Post subject: Reply with quote
haridevender wrote:
Hi
Thanks and Regards
Hari Devender
You have to consider both the load cases and takeout the critical out of them for individual members. Because load profile is entirely different in Spectrum case and static case. Simply making equivalent Base shear will not serve the purpose.
haridevender
PostPosted: Thu Jun 06, 2019 10:41 am    Post subject: Reply with quote
Thanks Sir for your reply.
Will you please let me know the literature for which both cases to be considered in analysis and design.
Hari Devender
rojanmathewtsy
PostPosted: Mon Jun 10, 2019 10:21 am    Post subject: Reply with quote
Actually, Response Spectrum analysis will give you results without any direction or the results will be positive due to modal combinations. So we are using both the methods to do the design. But, I think theoretically, if you are doing a dynamic analysis, then you don't have to follow static analysis. Other experts can shed some light on this.
Note: Response spectrum is not a full fledged dynamic analysis. It is basically static lateral load analysis of individual modes using a design spectra and combining them using proper modal combinations to get peak responses.
Rojan Mathew