Seismic / Earthquake Load Combinations for structures/Buildings
haridevender
PostPosted: Tue Jun 04, 2019 6:41 am    Post subject: Seismic / Earthquake Load Combinations for structures/Buildings Reply with quote
1.     DL+LL+EQ Combinations
1. In EQ load: it is a function of DL+ Partial LL, when considering in the above combination, LL shall be Part LL or full LL? Suppose EQ load is Ah x (DL+0.25 LL), then in the combination, LL shall be 0.25 LL or 100 percent LL?
2.     DL+EQ or DL+LL+EQ Combinations
As we are doing response spectrum analysis after enhancing the base shear, is it be necessary to consider static EQ or Dynamic EQ (Spec) in load combinations or both? Why?
Hari Devender
sakumar79
PostPosted: Tue Jun 04, 2019 7:36 am    Post subject: Reply with quote
    For Q1, IS 1893 2002 code allowed usage of reduced LL in the load combination. This has been removed (disallowed) in 2016 revision.
   Not sure I understand Q2. Please explain.
Yours sincerely
Arunkumar
haridevender
PostPosted: Tue Jun 04, 2019 8:19 am    Post subject: Reply with quote
Dear Sir
My Question number 2 is in  DL+EQ or DL+LL+EQ Combinations, whether we need to consider static EQ or Dynamic EQ (Spec) ? Why?
Hari Devender
rojanmathewtsy
PostPosted: Thu Jun 06, 2019 7:12 am    Post subject: Re: Seismic / Earthquake Load Combinations for structures/Buildings Reply with quote
As per IS code, Reduction is live load is applicable to Eq load calculation, not in the load combination.
For your second question, you have to consider both static and dynamic cases and take out the critical out of that for individual members.
rahul.leslie
PostPosted: Tue Jun 11, 2019 7:45 am    Post subject: Reply with quote
There are criteria in IS:1893 for deciding on which method to use: very limited ones for static cases. However, there is a confusion under certain peculiar conditions, as posted in https://www.sefindia.org/forum/viewtopic.php?t=19813
however, generally for multi storied buildings, I presume that Response spectrum be followed for buildings not falling under "regular buildings with height less than 15 m in seismic zone II", I presume. But the forces need to be scaled for Base-shear correction if required, and that's where criticality of the static method vs dynamic method is incorporated in the procedure.
Yogesh.Pisal
PostPosted: Tue Jun 18, 2019 9:27 am    Post subject: Reply with quote
Your first question is already answered by Arunkumar. Provision for reduction of LL factor in load combination is not suggested by revised code IS1893 Part 1 2016.
Second Question: Whenever you are carrying out dynamic analysis with or without shear enhancement, you shall use dynamic analysis load case (response spectrum load case) for combination.
Best Regards,
Yogesh Pisal
FARA
PostPosted: Thu Jun 20, 2019 12:17 pm    Post subject: Reply with quote
Yogesh.Pisal wrote:
Your first question is already answered by Arunkumar. Provision for reduction of LL factor in load combination is not suggested by revised code IS 1893 Part 1 2016.
Best Regards,
Yogesh Pisal
Yogesh Sir,
Can you share clause of 1893 from 2002 n 2016, where the LL shall be taken as reduced n 100% respectively .
sakumar79
PostPosted: Thu Jun 20, 2019 1:16 pm    Post subject: Reply with quote
   Clause 7.3.3 in IS 1893 Part 1 2002 code allowed the reduction of live load in load combinations. This clause has been removed in latest (2016) revision.
Hope that helps
Yours sincerely
S Arunkumar
sukanta.adhikari
PostPosted: Fri Jun 21, 2019 5:20 am    Post subject: Reply with quote
Dear sir
As per IS 875 Part 5:1987(Reaffirmed 2013),clause 8.1,reduction in live load is permitted both while generating seismic mass as well as during combination.The code is still active
Clause 8.1  Load combination
Note 3 - Whenever imposed load (IL) it combined with earthquake load (EL), the appropriate part of imposed load as specified in IS: 1893-1984 should be used both for evaluating, earthquake effect and for  combined load effects used in such combination.
S Adhikari
 Filesize:  70.45 KB
 Viewed:  59 Time(s)
hemal
PostPosted: Fri Jun 21, 2019 11:30 am    Post subject: Seismic / Earthquake Load Combinations for structures/Buildings Reply with quote
Dear Mr. Arunkumar,
Does it overrule clause 8.1, footnote 3 of IS 875 part 5?
Hemal Mistry
Sent from Yahoo Mail on Android