Assesment of Size Stone Masonry Foundation

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
prash1730
SEFI Member
SEFI Member


Joined: 02 Jul 2008
Posts: 5

PostPosted: Thu Nov 21, 2019 2:45 pm    Post subject: Assesment of Size Stone Masonry Foundation Reply with quote

Dear All,
I have been assigned to assess the existing Size Stone Masonry foundation for a 40 year old structure from one of my client and check the feasibility of adding another floor.

Details are as below:
Depth of foundation below GL.      - 3'-6"
PCC Depth                         - 0'-6"
1st Course                         - 2'-6" wide 1'-6" deep
2nd Course                    - 2'-0" wide 1'-6" deep
3rd Course (Above GL)          - 1'-6" wide 1'-6" deep

Load Details:
Ground floor Brick wall          - 9" wide 3m high clear
Ground floor roof               - 6" thick
First floor Brick wall               - 9" wide 3m high clear
first floor roof                    - 6" thick


No much wind load is present.
Seismic Zone - Bengaluru

I referred IS 1905 - 1987 and SP20. However, could not conclude on the details presented there. Request all sefians to help in this regard.

Further, it would be helpful if someone can share any rule of thumb to check the no. of courses of footing, width of footing per storey etc. it would be really helpful.

Best Regards,
Prashanth P N



Warning: Make sure you scan the downloaded attachment with updated antivirus tools  before opening them. They may contain viruses.
Use online scanners
here and here to upload downloaded attachment to check for safety.
SSM FOUNDATION.pdf
 Description:
SSM FOUNDATION

Download
 Filename:  SSM FOUNDATION.pdf
 Filesize:  28.23 KB
 Downloaded:  280 Time(s)

Back to top
View user's profile Send private message
es_jayakumar
General Sponsor
General Sponsor


Joined: 24 Nov 2011
Posts: 1408
Location: Cochin

PostPosted: Sat Nov 23, 2019 2:33 am    Post subject: Reply with quote

First and foremost, you have assess the maximum pressure on the soil from your footing, taking into consideration the eccentricity of the loading on it by the wall in the superstructure also. Check this against the SBC of the soil. Hence, you have first to assess the DL & LL coming on footing from the 2 storey building, per metre run of the footing. Your footing configuration looks fine.

E S Jayakumar
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy