50M DIA WATER TANK
husseins20
PostPosted: Mon Jan 27, 2020 1:19 pm    Post subject: 50M DIA WATER TANK Reply with quote
Dear Experts,
Can you please share your advise on the following situation:-
50m Diameter and 9m High RC Circular Tank. Resting on Ground.
Kindly advise if the wall is to be designed as proped cantilever and hoop tension or it will only have either of one only considering it H to D ratios.
Also some reference whereby similar tank example is furnished will be helpful
rgds
Hussein
PostPosted: Thu Jan 30, 2020 5:05 pm    Post subject: Reply with quote
Is your tank covered with roof slab at top ? Is the bottom of side wall constructed monolithic with base slab ? It will be ideal, if you can post a sketch of the layout of the tank showing the structural arrangements.
kawshik9
PostPosted: Fri Jan 31, 2020 6:02 am    Post subject: Reply with quote
Er. Hussein,
1) In case base of tank is fixed, as the Diameter of tank is very large when compared to height of the tank, hoop stresses are very small and tank wall acts more like cantilever.
2) If the base joint is flexible, Hoop stress will be maximum at the bottom and it will govern the design.
3) As the tank is of huge size, its better to model it in STAAD or some other analysis tools and design accordingly.
I am sending water tank design chapter for your reference(Refer ch.22 page -11 for circular tank design)
Ramakanth
RCC-WaterTanks (1).pdf
 Filename:  RCC-WaterTanks (1).pdf
 Filesize:  3.47 MB
 Downloaded:  161 Time(s)
PostPosted: Sun Feb 02, 2020 12:39 am    Post subject: Reply with quote
Er Hussain,
For furnishing a detailed answer, the structural arrangement of the tank is necessary to be posted. But, nothing is heard from you since. For large tanks (reservoir type), the side walls and base slab can be designed similar to cantilever retaining walls. Is the top of the tank is proposed to be covered with either dome with ring beam or slab & beam supported on internal columns ? This will determine if the top of the side wall is free or propped.
PostPosted: Thu Feb 06, 2020 12:11 am    Post subject: Reply with quote
Er. Hussain,
In the absence of any communication from you, I have worked out stresses / BM for the tank assuming side wall fixed at base & free at top and 500mm thick wall, using STAAD and IS Code coefficients. This is purely for illustration purpose. You can modify the attached STAAD file to alter the support conditions and thickness of the wall, if necessary.
                                     STAAD                 IS 3370 : IV
     Max Hoop tension     865 kN/ m                850 kN/ m
     Max BM                     195 kN-m                       231 kN-m
     Max Shear                  161 kN/m                   207 kN/ m
You can refer the following worked out examples, for more details on design :
1. Ex18.3 of Reinforced Concrete Vol.II by HJ Shah (Charotar)
2. Ex.10.4 of Design of Reinforced Concrete Structures by ML Gambhir (PHI)
Also refer this link to SEFI  :
https://sefindia.org/forum/viewtopic.php?t=16484&postdays=0&postorder=asc&start=0&sid=d5436854d15af80207e0638ee9b05ea2
TANK.rar
 Filename:  TANK.rar
 Filesize:  20.88 KB
 Downloaded:  98 Time(s)
thirumalaichettiar
PostPosted: Mon Feb 10, 2020 12:29 pm    Post subject: Reply with quote
Why not FLAT SLAB SYSTEM   can be used for the above tank since the dia is large say 50m and height is 9m?
T.Rangarajan
PostPosted: Mon Feb 10, 2020 12:45 pm    Post subject: Reply with quote
Certainly  !
But the questioner is silent, after raising the question !
husseins20
PostPosted: Fri Feb 14, 2020 9:28 am    Post subject: Reply with quote
Dear Eng. Jayakumar,
Apologies for the delay in response as was out of station.
Your valued input is really appreciated. The tank is eventually required to be covered. Cover can be shallow dome or beam slab.
rgds
Hussein