Posted: Fri Sep 25, 2020 11:48 am Post subject: Slab design with wall load |
|
|
Dear All,
How to design the two way slab when the wall load in coming on the slab?
I have attached the image of the slab.
Please guide me how to design this kind of slab.
Regards,
Ramu.
Description: |
|
Filesize: |
9.71 KB |
Viewed: |
51 Time(s) |

|
|
|
Back to top |
|
 |
renju mathew SEFI Member


Joined: 18 Feb 2016 Posts: 15
|
Posted: Sun Sep 27, 2020 2:36 am Post subject: |
|
|
Dear ramu,
This slab spans much bigger. So, if the slab is discontinuous on all four edges, then the thickness of slab will be 150mm and rebars - 12 mm dia Bars at 175 mm C/C on towards both directions. This design is uneconomical in my point of view. so you might consider splitting this slab into two by providing a beam under that wall which comes over the slab.
You can provide concealed beams under the walls if the distance between the wall and the support is less than 2 m. in this case, i think its not possible.
|
|
Back to top |
|
 |
es_jayakumar General Sponsor

Joined: 24 Nov 2011 Posts: 1382 Location: Cochin
|
Posted: Sun Sep 27, 2020 5:45 am Post subject: |
|
|
As pointed out by Er.Renju Mathew, you have to provide sufficient depth to the slab, considering its large span (4.8m). As advised by him, try to introduce a beam below the proposed wall. If there is no door opening in the wall, you can choose to make the beam up-standing also, should you want to avoid the unsightliness of the beam projection beneath. If you cannot try light weight partitions (wooden, aluminium, AAC block etc.) for the wall, use half-brick wall. If the supporting beam has to be done away with, you have to analyse the two-way slab using "Pigeaud"s Curves". A worthy worked out example for a similar case can be found in the book "Design of Reinforced concrete Structures" by Ashok Kumar Gupta (Galgotia Publications). I think, this book is out of print now. You can analyse the slab using STAAD also, by modeling the it using plate elements. Don't forget to check the deflection of the slab.
E S Jayakumar
|
|
Back to top |
|
 |
ramu_se SEFI Regulars

Joined: 30 Oct 2017 Posts: 36
|
Posted: Sun Sep 27, 2020 8:37 am Post subject: |
|
|
Thank you Renju sir and Jayakumar sir.
|
|
Back to top |
|
 |
ramu_se SEFI Regulars

Joined: 30 Oct 2017 Posts: 36
|
Posted: Sun Sep 27, 2020 1:56 pm Post subject: |
|
|
Dear Jayakumar sir,
I have done staad model for the slab and got maximum deflection as 5.4mm.I have converted the wall load as nodal load and applied on the plate nodes.
Attached the loading details for your reference. Please correct me if anything wrong.
Regards,
Ramu.
Description: |
|
Filesize: |
254.25 KB |
Viewed: |
44 Time(s) |

|
|
|
Back to top |
|
 |
es_jayakumar General Sponsor

Joined: 24 Nov 2011 Posts: 1382 Location: Cochin
|
Posted: Sun Sep 27, 2020 2:12 pm Post subject: |
|
|
Please post the STAAD file.
|
|
Back to top |
|
 |
ramu_se SEFI Regulars

Joined: 30 Oct 2017 Posts: 36
|
Posted: Sun Sep 27, 2020 3:16 pm Post subject: |
|
|
Sir,Please find the staad file.
Warning: Make sure you scan the downloaded attachment with updated antivirus tools before opening them. They may contain viruses. Use online scanners here and here to upload downloaded attachment to check for safety.
|
Description: |
|
 Download |
Filename: |
Staad.rar |
Filesize: |
365.55 KB |
Downloaded: |
98 Time(s) |
|
|
Back to top |
|
 |
badamsundararao ...


Joined: 24 Dec 2009 Posts: 213 Location: KAKINADA ANDHRA PRADESH
|
Posted: Sun Sep 27, 2020 5:15 pm Post subject: BRICK WALL ON SLAB |
|
|
Design a beam to a width of 100mm+2x depth of slab,sothat,the wall load will be disbursed@45degrees ,with depth of beam from minimum depth as per deflection consideration,so that the beam depth may not affect much from Ambiance point of view. Use AAC blocks to reduce the Dead load.
|
|
Back to top |
|
 |
es_jayakumar General Sponsor

Joined: 24 Nov 2011 Posts: 1382 Location: Cochin
|
Posted: Mon Sep 28, 2020 2:12 am Post subject: |
|
|
ramu_se wrote: | Sir,Please find the staad file. |
Why have you taken the floor finish and partition loads in upward direction ?
Correct it, design the slab manually and post the details please.
E S Jayakumar
|
|
Back to top |
|
 |
ramu_se SEFI Regulars

Joined: 30 Oct 2017 Posts: 36
|
Posted: Mon Sep 28, 2020 10:04 am Post subject: |
|
|
I have analysed the beam in staad.
Beam size 400 width(100+2xdepth of slab)and 150mm depth since i have considered 150mm slab thickness
wall load - 3.15 kN/m
wall thickness- 150mm,AACblocks
We have to design this beam and provide reinforcement for 400mm wide beam inside the slab?
Please find the attached file.
Regards,