Wind Load calculation as per IS 875 Part-3
rahulranjan_31
PostPosted: Thu Sep 02, 2021 6:32 am    Post subject: Wind Load calculation as per IS 875 Part-3 Reply with quote
Dear SEFIans,
For a foot over bridge I want to calculate the wind force over the purlin, but as per table-6 (External pressure coefficients for pitched roofs of rectangular clad buildings) for h/w ratio i am confused if i should take the height from ground level or from top of girder level (i.e. walkway level).
Any suggestion would be highly appreciated and thank you in advance.
PostPosted: Thu Sep 02, 2021 8:16 pm    Post subject: Re: Wind Load calculation as per IS 875 Part-3 Reply with quote
rahul_ranjanprasad wrote:
Dear SEFIans,
Dear Er Rahul
In Table 6 of IS 875(Part 3): 2015, h is taken from the GL only and is clearly indicated in the drawings.
PostPosted: Sun Sep 05, 2021 8:48 am    Post subject: Reply with quote
The height at which roof spring level is located from GL is height h to be taken . It is already made clear by Dr NS  Sir.
Confusion to you occured , I think , due to foot bridge deck and roof forming a sheltered formation.
But it seems a case of open roof  without wall cladding and exterior wind coefficient needs to be plus/minus 0.7 as per IS.
PostPosted: Sun Sep 05, 2021 12:29 pm    Post subject: Reply with quote
Minor slip in earlier post , inconvenience regretted
The internal wind pr coefficient needs to be plus/minus 0.70 , as roof is open , no cladding from sides except railing posts and roof posts in a foot over bridge.
rahulranjan_31
PostPosted: Mon Sep 06, 2021 4:26 am    Post subject: Reply with quote
Thank you so much for your response sir. Actually that is the confusion which i am not clear about. Since bridge deck comes in between GL and roof truss level then why should we consider height from the GL for calculating external wind pressure coefficient.
PostPosted: Mon Sep 06, 2021 4:57 am    Post subject: Reply with quote
The bridge deck is also subject to external and internal wind pressure based on height h of deck from ground surface .
The stability of overall bridge structure under wind case , will get uplift force  (by summing up) from (I) wind pressures on deck (ii) wind pressure on walkway A type sloping roof.