ramu_se ...
Posted: Sun Jun 19, 2022 1:35 pm Post subject: Cantilever retaining wall |
Can we construct an L-shape cantilever retaining wall (without toe slab) to retain earth up to 10' height?
SBC of soil is 200 kN/m2.
The length of the retaining wall is 100' on all four sides.
Is it ok to construct a 100' length retaining wall without any column?
What is the maximum length of the retaining wall that can be constructed without any column support?
Kindly share any references to the design L-shape retaining wall.
Thanks & Regards,
Ramu.
vikram.jeet General Sponsor
Posted: Sun Jun 19, 2022 4:34 pm Post subject: |
Toe-less cantilever retaining wall
Cantilevered ret wall without toe can easily be constructed. The stabilizing weight is available from back fill soil . Base width (only heel slab ) can be fixed to provide required FOS against OVERTURNING as also Sliding , plus keeping Base pressure within SBC of founding strata.
However sometimes situation demand construction of Heel less retaining wall and it is very challenging as soil weight is not available. Sliding in this situation is a big problem and shear key is a must in such walls. It is also costly .
Whereas in case of Toe-less ret wall backfill causing EP also give remedy in form of stabilizing weight over heel , but in case of Heel - less wall such remedy is not available.
ramu_se ...
Posted: Mon Jun 20, 2022 4:39 am Post subject: |
Thank you, sir.
In this type toe less retaining wall, what is the maximum length of the retaining wall that can be constructed?
If we construct 100' length or above do we need to provide any intermediate support?
hsrai ...
Posted: Mon Jun 20, 2022 2:04 pm Post subject: |
ramu_se wrote: | what is the maximum length of the retaining wall that can be constructed? |
It can be any length.
ramu_se wrote: | If we construct 100' length or above do we need to provide any intermediate support? |
No.
You need to provide expansion joints.
What type of project are you handling?
You mentioned four sides.
_________________ H.S.Rai |
ramu_se ...
Posted: Tue Jun 21, 2022 5:12 am Post subject: |
Thank you, Sir.
Here I have attached the image for your reference.
The front area(100') of the site is 5' down from the road level and the end area(100') is 8' down from the road level.
To bring that to the road level we have to fill the earth by constructing the retaining wall all around the site and also the retaining wall shall be extended further up to 5' or 4' as a compound wall.
We are planning to construct toe less type of retaining wall with a stem thickness of 6" and a heel width of 12" and a depth 12"
Can we take 2' as the depth of the foundation and fill(up to 2') it with stones, and mud, and consolidate it to make the surface more rigid to use as a foundation, instead of taking the wall from 2' depth, can we construct the retaining wall (8') on the rigid surface? (to be economical).
Kindly guide me if this works well or let me know any other solution to make this economical.
10.18 KB |
Viewed: |
19 Time(s) |
18.25 KB |
Viewed: |
13 Time(s) |
Rahul Ganguli29 SEFI Member
Posted: Tue Jun 21, 2022 4:42 pm Post subject: |
Kindly provide the others soil property details please
ramu_se wrote: | Thank you, Sir.
Kindly guide me if this works well or let me know any other solution to make this economical. |
Posted: Wed Jun 22, 2022 2:42 am Post subject: |
As already enlightened by Prof HS Rai Sir, a retaining wall can be constructed for any length without column supports if designed as stem and base rcc monolithic and self stable .
In case of column supported (predominantly lateral for ep) retaining walls columns are required at 9 to 12' interval , these cols also go up for boundary wall.
In case of brick retaining wall either provide broad width self stable brick wall with offsets OR brick wall with rcc columns at 8 to 12 feet interval with horizontal rcc beams /bands at two three levels.
No need for expansion joint below GL but above , joints needs to be provided as per IS . Brick masonry walls about 10 to 15m, RCC walls 20 to 30m but pl see IS code on exp joints for conviction and correctness.
ramu_se ...
Posted: Wed Jun 22, 2022 4:42 am Post subject: |
Thank you Sir.