acpl_sefi ...
Posted: Thu Jul 21, 2005 12:04 am Post subject: Welding of steel |
Dear all,
I want to know-- what is the size of weld deposited on a pair of rebars being welded together in relationship to the weld electrode size. COnsequently what should be the length of lap (is there a minimum). Is this a prequalified weld as per AWS or any other standard. If more than one pass is required for welding (say 5mm electrode on a 25 dia bar) what are the precautions to guarantee the strength of the weld (3 passes etc.)
Vipul Ahuja
On Sat, 16 Jul 2005 inchak@tatasteel.com wrote :
Quote: | ************************************************* SEFI e-Conference on Steel Reinforcement from June 27 to July 17, 2005 ************************************************* Sponsored by TATA Steel *************************************************
Thanks for a very topical set of questions.
I proceed to briefly answer each one to the best of my ability. 1) Can normal HYSD bars and TMT bars be welded. Answer: Welding is permitted and, indeed, carried out. The proposed draft revision of IS: 1786 (available in the URL: http://www.bis.org.in/sf/ced/p_7303.pdf) brings more clarity to this subject. I quote the relevant clause
QUOTE 3.2.2 For welding of cold-worked deformed bars, the recommendations of IS 9417:1979ß shall be followed. NOTE - Till such time IS 9417 is revised to incorporate the requirements of Thermo-mechanically treated steel, the recommendations of IS 9417 shall also apply to thermo-mechanically treated steel with the provision that the temperature under clause 10.3.4 of IS 9417:1979 shall not exceed 200 Deg. C for subsequent beads. UNQUOTE
While this is going to bring complete clarity on this subject, we do not see the need to maintain an inter pass temperature of 200 Deg. C. TMT is tempered at a temperature of 550 deg.C or more and is stable with respect to mechanical properties at least upto that temperature. Rather HYSD bars (CTD?)attain their strength by cold working and are susceptible to losing their strength beyond 400 deg.C.
As a result, whatever welding parameter is good for CTD will be good for TMT as well. An attempt is on to get this suitably incorporated in the undergoing revision of IS:1786 specification.
2) If welded is permitted, what happens to steel due to heat treatment and what stress should be considered in design. Answer: If welding electrodes of matching strength is used, there is no loss of strength because of welding. However, the prevailing provisions of IS 456 need to be complied with.
QUOTE 26.2.5.2 Strength of welds The following values may be used where the strength of the weld has been proved by tests to be at least as great as that of the parent bar. a) Splices in compassion - For welded splices and mechanical connection, 100 percent of the design strength of joined bars. b) Splices in tension 80 percent of the design strength of welded bars (100 percent if welding is strictly supervised and if at any cross-section of the member not more than 20 percent of the tensile reinforcement is welded). UNQUOTE
3) Some Steel companies claim their bars can be welded, what is their composition / speciality Answer: Again one needs to address this question within the boundaries of IS: 1786. Note 1 of clause 3.2 (page 6, stipulates :
QUOTE For guaranteed weldability, the percentage of carbon shall be restricted to 0.25 percent, maximum. UNQUOTE
Further Amendment No. 2 of May 2002 says QUOTE Note 1 - For guaranteed weldability, the Carbon Equivalent using the formula ............ shall be not more than 0.53 percent, when micro alloys/low alloys are used. When micro alloys are not used, Carbon Equivalent using the formula ........... shall be not more than 0.42 percent. Reinforcement bars/wires with higher Carbon Equivalent above 0.42 percent should, however be welded with precaution. Use of low hydrogen basic coated electrodes with matching strength bars/wires are recommended. UNQUOTE
4) Welding is a common practice in Piles and heavy engineering such as bridges etc. Answer: YES. It is also quite safe and extensively used abroad. We should have no hesitation in adopting this practice wherever it can add value. Hope you find the responses in order and satisfactory Thank you once again
Indranil Chakrabarti
The views, opinions, analyses and assessments contained herein do not necessarily reflect the views of SEFI or TATA Steel. Also SEFI and TATA Steel does not guarantee the accuracy of the data included in the proceedings of this e-conference and accepts no responsibility for any consequences of their use. ******************************************* ========powered by Reach1to1 Office Everywhere (http://www.reach1to1.com)====== |