100% + 30% Seismic Force consideration in Water Tank

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion
View previous topic :: View next topic  
Author Message
ankeshmundra1
SEFI Regulars
SEFI Regulars


Joined: 09 Sep 2011
Posts: 20

PostPosted: Thu Nov 03, 2022 10:54 am    Post subject: 100% + 30% Seismic Force consideration in Water Tank Reply with quote

Hello Everyone,
it is my query with respect to water tank seismic force consideration.
IS1893:2014(Part2) recommends Consideration of force in critical direction or Apply 100%+30% Rule.

Critical Direction of force is suggested by IITK EQ-08.

My Question is -
If in the design i am considering force direction as per atatcehd fig.( IITK EQ-0Cool, do i also need to apply 100%+30% Rule.

Is there any IS/BS/ACI code/Paper which is in support of this ?



IITK-Water Tank.png
 Description:
 Filesize:  90.98 KB
 Viewed:  17 Time(s)

IITK-Water Tank.png


Back to top
View user's profile Send private message
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3625

PostPosted: Fri Nov 04, 2022 3:01 am    Post subject: Reply with quote

Just a personal viewpoint

Irrespective of provisions , it is better to check the important  structures like Overhead water tanks  for the structural stability & safety  ,  components adequacy .

100% EQ (x horz*)+ 100% EQ (y vertical )
(* str being symmetrical in plan about center point , EQ z horz  need not be checked)

100% EQ (x ) + 30% EQ ( z) + 30% EQ(y)


Also please refer IS code IS 11682  on ' CRITERIA FOR DESIGN OF RCC  STAGINGS FOR OVERHEAD WATER TANKS '.
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> SEFI General Discussion All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy