Flat slab Load transfer Mechanism

 
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> Er. T. Rangarajan
View previous topic :: View next topic  
Author Message
ramu_se
...
...


Joined: 30 Oct 2017
Posts: 111

PostPosted: Wed Jun 28, 2023 4:13 pm    Post subject: Flat slab Load transfer Mechanism Reply with quote

Dear Sir,

Kindly explain how the load is getting distributed in flat slabs to the supporting columns.

Thanks & Regards,
Ramu.
Back to top
View user's profile Send private message
Thankful People
1 user(s) is/are thankful for this post.
vikram.jeet
General Sponsor
General Sponsor


Joined: 26 Jan 2003
Posts: 3946

PostPosted: Fri Jun 30, 2023 3:40 am    Post subject: Reply with quote

Flat slab :- As all we know it is beam less slab, slab in itself act  as beams in two directions .

Slab is treated to be divided into Column strips and middle strips, in both directions  ,Refer code IS 456 .

Every thing is explained in IS.

Though transfer of load becomes two way at columns ,, Bending moments are worked out in each direction assuming one way action since each side strength to transfer loading is dependent on other direction  strength of flat slab.

Slab is assumed to be divided into Column strips and Middle strips

There are two methods of analysis :
Direct Design Method
Equivalent frames method

DDMethod :-
Minimum three spans inbeach dir for this method
Absolute mo Mo:-
W= w*Lx*Ly
Absolute BM x =W*Lnx/8
Absolute BM y = W*Lny/8
In absence of column heads Lnx= Lx and Lny=Ly
In case of drops /col heads = Ln is clear span between drops, brackets but not less than 0.65*L

+ve and  -ve Moment allocation :-
-ve Moment = 0.65*Mo
+ve Moment = 0.35*Mo

Moment allocation to strips :-
Column strips (Acting as concealed beams)
-ve moment:-
-ve moment at support for column strip := 0.75 of (0.65*Mo)
-ve moment for Middle strip  = remaining ie 0.25 of (0.65*Mo

+ve moment

+ve moment for Column strip  = 0.60 of (O.35*Mo)
+ve moment for mid strip = O. 40 of (O.35*Mo)

This above is for Internal Panels,,
For external refer code

(To be continued)
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topicReply to topic Thank Post    www.sefindia.org Forum Index -> Er. T. Rangarajan All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy