Posted: Thu Oct 05, 2023 6:33 pm Post subject: ISOLATED SQUARE FOOTING DESIGN |
|
|
How to design ISOLATED SQUARE FOOTING under a biaxial column??
We generally consider service axial load then check for one way and two-way shear and design flexural reinforcement.Whether we need to take the biaxial moment in column while designing FOOTING? If yes then how to do it? |
|
Back to top |
|
 |
sakumar79 ...

Joined: 18 Apr 2008 Posts: 711
|
Posted: Fri Oct 06, 2023 2:08 am Post subject: |
|
|
Dear Er Amrutha,
The footing size is calculated by finding the pressure at the four corners of the footing as P/A +/- Mx/Zx +/- My/Zy. If the lowest value is more than 0 and the highest value is less than SBC, then the footing size is okay. Once the size is confirmed, design load of Max Pressure x A /1.1 can be considered as Axial Load for footing thickness and reinforcement design.
Hope that helps
Arunkumar |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3738
|
Posted: Fri Oct 06, 2023 3:58 am Post subject: |
|
|
Nicely explained by Er Arun,,
In case some economy in footing size desired,, then Some upliftment of footing can be taken,, about 20% on Firm soil /rock strata and lesser in medium and poor soils UNDER NORMAL CASE and 33% upliftment of footing area under Wind /Eq Cases.
However for Bridges,, No upliftment of footing area permitted
For foundations resting on Soils, but for Foundations on Rock it is permitted as stated above.
You can refer Teng's Charts for Design of Footings subject to bisxisl moments with upliftment of footings as given in book ' The Foundations Design by Wyane C Teng'
Last edited by vikram.jeet on Fri Oct 06, 2023 4:05 am; edited 1 time in total |
|
Back to top |
|
 |
vikram.jeet General Sponsor

Joined: 26 Jan 2003 Posts: 3738
|
Posted: Fri Oct 06, 2023 4:00 am Post subject: |
|
|
In continuation to above post :-
However Maximum base pressure shall be within permitted Sbc |
|
Back to top |
|
 |
amrutha_N SEFI Member

Joined: 29 Mar 2019 Posts: 4
|
Posted: Fri Oct 06, 2023 6:26 am Post subject: |
|
|
Thank you Er.Arun .Checking for SBC WITH maximum pressure takes BIAXIAL MOMENT into account for the design of FOOTING. Will you say how to Assume SBC OF SOIL IN a place without SPTvalue . Given the depth of FOOTING to be 5feet below GL??? |
|