Restriction on unbonded surface in a Constrution joint
santhu256
PostPosted: Fri Jan 12, 2024 4:44 am    Post subject: Restriction on unbonded surface in a Constrution joint Reply with quote
Hi All,
I'm seeking some guidance with the subject.
I am a Technical Engineer in a company dealing with Sacrificial Formwork(Stremaform),which is a metal mesh designed to use in construction joins.
When the engineers specify a hydrophilic(Waterstop) we provide a metal strip in the center of Stremaform. We have a guideline regarding the size of the plate. I was searching for any code provisions or guideline regarding  restriction on the area of unbonded surface in a Construction joint.
If anyone has knowledge in this area or could direct me to relevant resources or standards, it would be immensely helpful. Sharing your expertise or pointing me to where I can find such information would be greatly appreciated.
Santhosh.
PostPosted: Fri Jan 12, 2024 6:38 am    Post subject: Reply with quote
Not sure,, but pl check with FINTEL HANDBOOK,,
I think one chapter is available.
Also you may refer IS 3370 Part 1 & part 2.
santhu256
PostPosted: Mon Jan 15, 2024 6:58 pm    Post subject: Thanks Reply with quote
mjnasar
PostPosted: Thu Jan 25, 2024 2:12 pm    Post subject: Reply with quote
HI santhu256
Greetings
As per ACI318-19 22.9—Shear friction
at construction joint the  ultimate shear forces at the our section
should be transfer by shear friction
Phi Vn  > Vu ---(22.9.3.1)
the Vn should be calculated
Vn =  coefficient Avf  fy  ----(22.9.4.2)
and should not be more than
Vn =  0.2  *  fc * Ac   ----(22.9.4.2)
as our case , we have the unbonded concrete area & steel bars which are not embedded in concrete
so calculate the Vn with reduced concrete section area and Vn with reduced steel area
and minimum of Vn should be more than the ultimate shear force at the construction Joint .
I hope this will help you.
best regards
linkedin.com/in/mjnasar