Punching shear reg

 
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conferences-2008 [ Flat Slab Design issues ]
View previous topic :: View next topic  
Author Message
kishku4u
SEFI Regulars
SEFI Regulars


Joined: 06 Aug 2008
Posts: 37

PostPosted: Wed Dec 24, 2008 3:49 am    Post subject: Punching shear reg Reply with quote

Hi sir,

I have two doubts regarding

1)How can we calculate punching shear force around for an intermediate floor?

2)Is it necessary to consider beam shear?

Regard
Kishku
Back to top
View user's profile Send private message
mkalgal
Silver Sponsor
Silver Sponsor


Joined: 26 Jan 2003
Posts: 54

PostPosted: Wed Dec 24, 2008 5:20 pm    Post subject: Reply with quote

Dear Mr. Kishku
1. Calculation of punching shear is quite simple and is explained well in almost all the RCC books. One needs to
a. calculate the load contribution(say total load) from the slabs around the column,
b. calculate the load that directly passes into the column within the conical(pyramidal) area around the column
c. subtract it from the total load to get the load that causes punching shear.
d. to the above you need to add the shear transferred due to unbalanced moments (or lateral load action)at the column-slab interface to get the total shear at the critical sections.
e. there is no difference in the method whether the slab is intermediate floor or top floor.
2. Beam shear is not to be confused with slab shear. Punching failure occurs only due to two-way shear in a slab column junction.

regards

Kalgal
Back to top
View user's profile Send private message
Display posts from previous:   
This forum is locked: you cannot post, reply to, or edit topics.This topic is locked: you cannot edit posts or make replies. Thank Post    www.sefindia.org Forum Index -> E-Conferences-2008 [ Flat Slab Design issues ] All times are GMT
Page 1 of 1

 

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You can attach files in this forum
You can download files in this forum


© 2003, 2008 SEFINDIA, Indian Domain Registration
Publishing or acceptance of an advertisement is neither a guarantee nor endorsement of the advertiser's product or service. advertisement policy