Posted: Mon Dec 22, 2008 8:34 am Post subject: Post tensioned slabs |
|
|
Hi All,
This is a question which is bothering me from a long time and I need some explanation for the same.
In all the post tensioned slabs I have come across, I find that the post tensioned tendons do not pass through the column; that is; whenever a column is encountered the tendons are either curved (in plan) so that they do not intercept the column(s).
I want to know whether my reasoning for the above (that is the reason for the tendons being curved (or) not directly passing through the column is correct:
1. The tendons are highly stressed to the order of 1600 MPa.
2. If the tendon pass through the column, we could imagine the free body of the column: it woild be : at the location where the tendon passes through the column there would exist an enormous point force acing on the column which indeed would cause the bending of the column which could be detrimental.
3. I want to know if my interpretation/intuition of the above scenario is correct?
Can anyone please comment on my thinking above?
Please help! |
|
Back to top |
|
|
Thankful People |
2 user(s) is/are thankful for this post.
arajesh(22-12, 10:45), admin(25-12, 11:58), Thanks kajal.chopra for his/her post
|
|
sahi SEFI Member
Joined: 02 Oct 2008 Posts: 4
|
Posted: Mon Dec 22, 2008 8:58 am Post subject: Post tensioned slabs |
|
|
For Interior col. take them straight. For end column if not
practicable U may curve then. Col. + Slab act as monolith concrete
unit. No concenteration of forces due to cables.
On 12/22/08, kajal.chopra <forum@sefindia.org> wrote:
Quote: | Hi All,
This is a question which is bothering me from a long time and I need some
explanation for the same.
In all the post tensioned slabs I have come across, I find that the post
tensioned tendons do not pass through the column; that is; whenever a column
is encountered the tendons are either curved (in plan) so that they do not
intercept the column(s).
I want to know whether my reasoning for the above (that is the reason for
the tendons being curved (or) not directly passing through the column is
correct:
1. The tendons are highly stressed to the order of 1600 MPa.
2. If the tendon pass through the column, we could imagine the free body of
the column: it woild be : at the location where the tendon passes through
the column there would exist an enormous point force acing on the column
which indeed would cause the bending of the column which could be
detrimental.
3. I want to know if my interpretation/intuition of the above scenario is
correct?
Can anyone please comment on my thinking above?
Please help!
|
Posted via Email |
|
Back to top |
|
|
ahujavipul General Sponsor
Joined: 26 Jan 2003 Posts: 230
|
Posted: Mon Dec 22, 2008 9:48 am Post subject: Post subject: Post tensioned slabs |
|
|
In the Indian scenario we usually use wide ducts comprising 3, 4 or 5 tendons whose total width is approx 70 mm. Usually in a ductile detailed column there is not enough space to accommodate this width. I have been trying to tell manufacturers to provide single tendon ducts so at least a few can be accommodated.
The stress in steel is high but not so in concrete (approximately 2 to 3 MPA).
Bending of column & its interaction with the slab is accounted for in design.
Hope that answers your questions
Regards
Vipul Ahuja
**************
Hi All,
This is a question which is bothering me from a long time and I need some explanation for the same.
In all the post tensioned slabs I have come across, I find that the post tensioned tendons do not pass through the column; that is; whenever a column is encountered the tendons are either curved (in plan) so that they do not intercept the column(s).
I want to know whether my reasoning for the above (that is the reason for the tendons being curved (or) not directly passing through the column is correct:
1. The tendons are highly stressed to the order of 1600 MPa.
2. If the tendon pass through the column, we could imagine the free body of the column: it woild be : at the location where the tendon passes through the column there would exist an enormous point force acing on the column which indeed would cause the bending of the column which could be detrimental.
3. I want to know if my interpretation/intuition of the above scenario is correct?
Can anyone please comment on my thinking above?
Please help! |
|
Back to top |
|
|
kajal.chopra ...
Joined: 26 Jan 2003 Posts: 102
|
Posted: Mon Dec 22, 2008 10:33 am Post subject: |
|
|
Thanks for the reply.
You said , in a ductile detailed column, there is not enough space to accomodate the width of (say) 70 mm.
Let us there is a provision to accomodate that width of 70mm(supposing),
then if these tendons do pass through the column would not that high force exerted on that location of the column by the tendon cause column to bend heavily?
Would not this be detrimental for the column?Would not this effect be avoided by not passing the tendon through the column (assuming there is sufficient space for the duct to pass)? |
|
Back to top |
|
|
kajal.chopra ...
Joined: 26 Jan 2003 Posts: 102
|
Posted: Mon Dec 22, 2008 11:13 am Post subject: |
|
|
What I mean to say is that in order to avoid the bending of the column is it not better to avoid passing the tendon through the column? |
|
Back to top |
|
|
cancer_kk SEFI Member
Joined: 03 Oct 2008 Posts: 6
|
Posted: Mon Dec 22, 2008 12:32 pm Post subject: Post tensioned slabs |
|
|
Dear kajal,
I hope that passing of tendons through should not cause you worry about column bending,because what I feel that cosine part of the postensioning force in tendon actually compensate for shear as well bending.
further if I am not wrong, Even if one avoid tendon to pass through column,passing of moments to columns from tendons through distribution cant be avoided.
On Mon, 22 Dec 2008 kajal.chopra wrote :
Quote: | What I mean to say is that in order to avoid the bending of the column is it not better to avoid passing the tendon through the column?
|
Posted via Email |
|
Back to top |
|
|
ahujavipul General Sponsor
Joined: 26 Jan 2003 Posts: 230
|
Posted: Mon Dec 22, 2008 6:45 pm Post subject: Post tensioned slabs |
|
|
It is not only desirable but actually required by some codes to run tendons thru the column cage (for ductility of the column-slab connection). Further additional bottom steel is also required to prevent progressive collapse.
The concern for column bending is academic. This is accounted for in design. However very stiff columns or shear walls must be isolated from the PT operation-- say by casting in 2nd stage after the PT operation.
Regards
Vipul Ahuja
***********************
What I mean to say is that in order to avoid the bending of the column is it not better to avoid passing the tendon through the column? |
|
Back to top |
|
|
kajal.chopra ...
Joined: 26 Jan 2003 Posts: 102
|
Posted: Mon Dec 22, 2008 7:19 pm Post subject: |
|
|
You mean the bending moment induced in column due to tendons running through the column is accounted in design of the column?Through which clause of IS 456 or IS 1343? |
|
Back to top |
|
|
kajal.chopra ...
Joined: 26 Jan 2003 Posts: 102
|
Posted: Wed Dec 24, 2008 4:19 am Post subject: |
|
|
My only concern is:
Let us say a tendon passes through the olumn.
Now imagine the free body of the column.
In its free body, there would be a huge concentrated force acting at the location where the tendon passes, right?
Thus, this single concentrated force can cause enormous bending in the column irrespective if the stiffness of column is high/low)
Please anyone - throw some light on this issue. |
|
Back to top |
|
|
Kedar SEFI Regulars
Joined: 23 Jul 2008 Posts: 32 Location: Mumbai
|
Posted: Wed Dec 24, 2008 6:02 am Post subject: |
|
|
Hi Kajal
Can you please specify
1.eccentricity of tendons wrt column centre
in horizontal or vertical plane?
Lets calculate roughly the force applied by
tendon on column
1.Let's assume only tendons(say 4 nos 13mm dia stressed to 1000MPa)
are passing through column (say 900x900)with eccentricy if 400 mm (max
we can take ! )from centre of column.
2.Let's assume tendons are bent in horizontal plane by 6 dgrees for
all practical purpose wrt the direction of cable from its origin.
3.Let's assume tendons are bent in vertical plane by 4 dgrees for all
practical purpose wrt the horizontal plane. for slabs this is a bit
conservative.
4.Force in cables=no of cable x area x stress
=4 x 133 x 1000=532000 N = 532 kN ~ 53 Ton
5.Lets calculate forces due vertical dip by resolving forces
5a.Vertical component = Force in tendons x sin(theta)
=532 x sin(4)~ 37.5 kN
5b.Horizontal component = Force in tendons x cos(theta)
=532 x cos(4)~531 kN
6.The force transfer mechanism due profile in vertical plane
6a.Vertical components
Moment induced in column = vertical component in tendon x eccentricity
in column section
= 37.5 x 0.4 = 15.0 kN.m for all practical purpose this a small
if you want you can account for it with other LCs.
Please note that this the worst case we assumed that cables are
concentrated at one point/line but in actuals the are seperated by
some distance hence actual moments induced due to cable eccentricity
is low.
6b.Horizontal Component
The force is passed from column to slab due to diphragm action(since
column slab are integrally casted)the inplane rigidity of slabs we can
safely assume infinite.Hence the more number of columns this force is
shared less by every column.In most cases/practical the forces are
cancelled out by considering other tendons in the system.
7.Lets calculate forces due horizontal turning of tendons.
Here whatever forces/components are generated due to bend all are
transferred in diaphragm action in slab.We can safely apply same logic
of point No 6b.
I hope possibly this would solve your querry regarding moments induced
in column due to bend in tendons.In single word in most of the case
they are trivial for all practical purpose? but needs to be assess on
case-to-case basis.
Please correct me if I am wrong.
Regards
Kedar |
|