Upstand beams
bkkk
PostPosted: Fri Dec 31, 2010 10:09 am    Post subject: Upstand beams Reply with quote
Dear  sefians
While designing an up stand beam, where slab joins the beam at beam bottom,can we adopt the effective depth as  for a normal beam,what are the factors that are needed  to be considered while designing   such beams.
Er.Balaji venkateswaran
gpsarathyy
PostPosted: Fri Dec 31, 2010 12:30 pm    Post subject: Reply with quote
Dear Mr. Balaji,
I think you are referring to the inverted T-beam.
The design is similar ordinary T-beam, only effective width of Tee beam to be calculated, it depends on the other factors like the length of the span, width of the beam and the c/c to span of the beam.
I hope it clarifies your doubt.
G.Parthasarathy M.E. (Structural Engg.,)
Chennai.
Email: gpsarathyy@gmail.com
umeshrao
PostPosted: Fri Dec 31, 2010 12:48 pm    Post subject: Re: Upstand beams Reply with quote
bkkk wrote:
Dear  sefians
While designing an up stand beam, where slab joins the beam at beam bottom,can we adopt the effective depth as  for a normal beam,what are the factors that are needed  to be considered while designing   such beams. Er.Balaji venkateswaran
     Dear Mr. Balaji,
     Unless this beam is cantilevered, you can treat this beam as normal beam. If the beam is cantilever, then slab at bottom will be compression face then you may design as T beam.
     Regards Umesh Rao
PostPosted: Sat Jan 01, 2011 4:32 am    Post subject: Upstand beams Reply with quote
Upstand beam for sagging moments will be a rectangular beam
but for hogging moments will be a T- Beam
Further to add that in upstand beam the hanging action of
slab loading shall be accounted by adding additional
area required for direct tension due to hanging
(though small) to the area worked for shear reinf.
best regards
vikramjeet
-- ญญ
umeshrao
PostPosted: Sat Jan 01, 2011 6:35 am    Post subject: Re: Upstand beams Reply with quote
[quote="vikram.jeet"]Upstand beam for sagging moments will be a rectangular beam but for hogging moments will be a T- Beam. Further to add that in upstand beam the hanging action of slab loading shall be accounted by adding additional area required for direct tension due to hanging (though small) to the area worked for shear reinf.
best regards vikramjeet
     Dear Vikramjeet,
     Very interesting note on shear. Though we have been using this thought for water tank beams/walls, where slab is hung from beam, to restrict tension in stirrups or vertical reinforcement in the wall. But never gave a thought for slab supported at the soffit of beams.
     May be,as you rightly said that this has to be considered for design of shear, it is not done for various reasons. Normally loads on slab are small, unlike water tank slab. And hence minimum shear reinforcement takes care.
     Thanks for the new thought[ atleast for me.], I will check next time and revert back.
     Regards Umesh Rao
shirishmehta3
PostPosted: Sun Jan 02, 2011 8:48 am    Post subject: Re: Upstand beams Reply with quote
best regards
vikramjeet
-- ญญ
Dear Sir
Can you please further clarify regarding this thought on shear??
I want to share my experience I faced once.
I was designing a flat slab structure having spans of 7-8m. The slab had peripheral inverted beams. I considered the following points while designing these beams for shear.
1) I calculated the shear force in the beam due to load transferred from slab and line loads due to facade. Say for a simply supported beam Vu= wl/2
Now, assuming a cold joint between the slab and the beam as it may be the case because of an upstand, I neglected the contribution of concrete in resisting shear as a weak plane is formed at the slab beam junction. Assuming the stirrups take this entire shear I got the value of Av.
2) As you said, these stirrups are subjected to direct tension in a way as the slab seems to hang from the beam. So I thought of checking whether the stirrup area Av obtained from item 1) stated above is sufficient to carry the 1-way shear from the slab. ( i guessed it should b the slab shear and not the beam shear... because the slab shear acts as a uniformly distributed load on the beam which will be transferred to the stirrup by means of direct tension). But to my dismay I found that this method leads to very high shear reinforcement Sad
I also went one step further to ensure that only the 1st outer leg of the stirrup takes this direct tension because it is not clear to me whether the crack would be intercepted by all stirrup legs or not during this transfer of shear by means of direct tension. This further led to an uneconomical design.
I am a bit lost in this method which i used as it was giving very high reinforcement. Although the transfer of forces as explained in both items above seem logically appropriate to me.
It would be indeed appreciable if anybody can comment on the approach used and point out the mistakes in my assumptions.
Shirish.
PostPosted: Mon Jan 03, 2011 5:06 am    Post subject: Upstand beams Reply with quote
Dear Er Sirish,
Your problem is in two parts
i) Transfer of shear from slab to upstand beam
ii) Hanging action of slab on upstand beam
(Cold joint is is rarely in practice since slab is cast with beams),
However taking to consideration of cold joint between slab and beam , the shear
between slab and beam will be transferred through the slab reinf bars through
dowel action and slab reinf entering the beam needs to be enhanced at
beam junction. Preferably Bottom bars shall be added with Ld embedment on
either side (and top bars as per original design for partial fixity w/o enhancement)
This would require accountal in shear reinf(i.e. stirrups) being provided in beam
Asv = area required for stirrups for spacing =S
due to SF =( w+w')L/2 where L is span of beam
w is the (self wt +any partition/facade load over beam) per m
and w' is load from slab per m
Addtional area in length of one meter from hanging action A1=[ w'/perm.stress]
perm stress in direct tension, probably this would be a small addtional since
Additional area required for spacing S cm= A1*S/100
For sake of simplicity , only working stress is used but problem can be
solved in limit design with appropriate LF and allowable stresses
best regards
vikramjeet
Dear Sir
Shirish.
-- ญญ
bkkk
PostPosted: Mon Jan 03, 2011 7:42 am    Post subject: Up stand beams -reg Reply with quote
Thank you Prtahsarathy sir, Umesh rao sir,vikramjeet sir and shirish sir for fruitful discussions and clarifications
umeshrao
PostPosted: Mon Jan 03, 2011 8:51 am    Post subject: Re: Upstand beams Reply with quote
[quote="shirishmehta3"]
vikram.jeet wrote:
Upstand beam for
Dear Sir
Dear Shirish,
[ I do hope you added equivalent shear due to torsion to vertical shear.]
     [ A weak plane assumed can only be for in-plane shear and hence stirrups will act as shear heads and take across shear and not as tension.This shear is moment in the beam divided by lever arm of beam. This shear will be carried by all legs of stirrups.]
[To Vs add tension caused by hanging of slab and then work back Asv and Sv.]
Shirish.
     Regards Umesh Rao
thirumalaichettiar
PostPosted: Sun Sep 17, 2017 4:57 am    Post subject: Reply with quote
UP-STAND BEAM
What id the EFFECTIVE FLANGE WIDTH for an up stand (inverted beam)? Is any guided value in IS 456-2000? Hope that there is no such guidance in IS code 456.
Please inform.
Er.T.Rangarajan